Electric Water Heater

Teken

Well-known member
Joined
Jan 2, 2010
Messages
8,214
Location
The Bad Lands
Hello,

As some of you may be aware I have been using a special tool to monitor my electrical consumption in the home. Recently, I have been trying to trouble shoot a few devices which I believe is not wired correctly.

I have a electric hot water tank and believe its 240. I also believe in most hot water tanks there is no neutral, correct?

On the electrical panel there is only two wires going into the dual pole 30 amp breaker. On the electric water heater there is one orange 10-2 NM wire powering up this monster tank.

My question is this: With the CT's (current transformers) to measure the total wattage on this appliance all I need to do is measure one of the service feeds correct?

Or, does both service feeds for that circuit need to be monitored to obtain a true reading?

I am having a brain fart at 5:48 AM so any insight would be appreciated!

Teken . . .
 
Last edited:
To avoid these ads, REGISTER NOW!

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
It's AC so you only need to measure 1 leg. Your measurement output is amps and you will need to know that your amperage is being consumed at 240 volts. Volts times amps equals watts.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,252
Location
Modesto, CA
It should be a balanced load so u only need to monitor one leg! If it needed a neutral like some 240v appliances have, then it would be different much like a utility meter operates! And 10-2 is the correct wire in case u were wondering!
 
OP
T

Teken

Well-known member
Joined
Jan 2, 2010
Messages
8,214
Location
The Bad Lands
It's AC so you only need to measure 1 leg. Your measurement output is amps and you will need to know that your amperage is being consumed at 240 volts. Volts times amps equals watts.

It should be a balanced load so u only need to monitor one leg! If it needed a neutral like some 240v appliances have, then it would be different much like a utility meter operates! And 10-2 is the correct wire in case u were wondering!

So after talking to the maker of the device. I have a couple of options to record and capture the wattage. I can leave both CT's on both feeds and accept that the wattage meter will show up on both.

I can use just one CT, and use the software to double up the wattage so both sides will be captured. But, only one of the GUI power meters will show the combined power being consumed.

I believe I will use the one CT approach and use the software to compensate and than display the combined load / power so it can be viewed.

Thanks Guys.

Teken . . .
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
240 two wire is simply power in and power out, no different than 120v is. Measuring current on both legs would double the number you are looking for. I cannot see why you would need more than one CT on one leg of the 240v for this.

Charles
 
To avoid these ads, REGISTER NOW!

Socophreak

Well-known member
Joined
Jun 18, 2010
Messages
231
Wattage does not double. Current is the same through both legs @ 240V. Both legs are 120V to neutral or ground, and 240V across each other.
 

Jim_No_Garage

Well-known member
Joined
Jan 15, 2011
Messages
3,343
Location
Millington NJ
Wattage does not double. Current is the same through both legs @ 240V. Both legs are 120V to neutral or ground, and 240V across each other.

Total wattage used would be double - wouldn't it? He wants to know total usage by the tank. Mesauring and calculating based on 1 leg is giving him 1/2 of the power used.

Teken - I'm jealous of the work you are doing in HA, monitoring and Solar collection.

My goal is to find a house or building - preferably something with some architectural appeal and take it back to the frame and do it up with modern amenities and materials.

The problem is that nothing stands still . . . so it's like hitting a moving target.

Cheers

Jim
 
OP
T

Teken

Well-known member
Joined
Jan 2, 2010
Messages
8,214
Location
The Bad Lands
Total wattage used would be double - wouldn't it? He wants to know total usage by the tank. Mesauring and calculating based on 1 leg is giving him 1/2 of the power used.

Teken - I'm jealous of the work you are doing in HA, monitoring and Solar collection.

My goal is to find a house or building - preferably something with some architectural appeal and take it back to the frame and do it up with modern amenities and materials.

The problem is that nothing stands still . . . so it's like hitting a moving target.

Cheers

Jim

Jim,

Yes, that is my goal and intent. A lot of this is new to me and I am trying to configure and wrap my head around all of these elements. I'm just trying to make sure what I am measuring, capturing is indeed correct.

If not I would like to correct any mistakes in my install. I would rather be wrong and be told so, and be allowed to learn and correct it.

Than, to live through the next *** years thinking all of this is wired and captured right.

I rather not live in ignorance of the facts and wanted some feed back from the GJ collective.

Let me post some images for all to see and maybe this will make more sense. Also, I was mistaken in stating there were (2) CT's measuring the electric hot water tank load.

There is only (1) CT in place. Based on what I have read and see at home this is normal and expected behavior. Below is a screen capture of what I see on the meter.

EDIT: I will need to wait for the water heater to come on to screen capture the power being consumed BRB.

Teken . . .
 
OP
T

Teken

Well-known member
Joined
Jan 2, 2010
Messages
8,214
Location
The Bad Lands
Just wanted to close off this problem as fixed. I know a lot of this is hard to translate to others who don't have the same equipment or understanding of what I am trying to do and see.

So I hope this link will provide some insight and clarify my intent. If you scroll all the way down you will see the images of what I was trying to accomplish. Trying to explain something is much harder than providing pictures to see.

http://garagejournal.com/forum/showthread.php?p=2977587#post2977587