In Santa Fe county New Mexico. Well water. Yeah I was expecting much worse when I was told what was paid for everything. As far as function never heard if it giving any problems or issues for the last 4 years it has been in use. As per county website plumbing code follows the UPC in the code bookhard to tell what is necessary due to you not posting a location.amazing price as the water heater costs over $200
I wouldn't want the Pressure/relief valve being piped somewhere else. If it's building up pressure, you want to be sure it gets out of there.
They are corrugated copper lines, it's insulation taped overGet a foot or two of copper attached to the heater cold and hot and the relief should be piped with a metallic pipe and down.Eliminate all of the roller coaster turns and neaten it up.Whats under the grey wrapped up lines coming out of the wall?
Is that really 14 gauge wire feeding the water heater? That is a huge fire hazard. 14 gauge is rated at 15 amps and a 5000w water heater will pull 22-25 amps usually. That needs to be corrected ASAP. Also is the water heater grounded? With the PEX connections it is no longer bonded to your water lines.
Where is that blowoff valve going to ?
She's a beaut Clark...
Worst part is the original lines would be fine if the water heater had top inlet and outlets.
When this water heater kicks the bucket you could go back to the same as original.
The way the piping for the T&P valve is arranged, it creates a trap and that is not allowed, it must be arranged to drain & not leave any water in the line.
Looks like #10 to me. Not sure where anybody is getting #14 from?
Where is that blowoff valve going to ?
Just point the pt straight down. No need to route it anywhere
Around here, the PT valve pipe has to go straight down and terminate within 4" of the floor.
Some local codes require water heaters to be on a pedestal (or is that just for gas ?). Also some codes require it to be strapped to wall (stud).