Electrical for Welders and Air Compressor

tlinz11x

New member
Joined
Jan 4, 2025
Messages
2
Hello Everyone,

I am looking to install two 240v outlets and a 120v 30A outlet to run welding machines and a Husky 3.7HP 60gal air compressor in my garage.

We own the home but plan to relocate in the next couple years. The panel is on the opposite side of the house, approximately 50 feet away. For these reasons, I am considering installing the outlets outside below the panel and running the equipment with heavy duty welding extension cords. Would only see use on the weekends when I'm not welding for the man.

My main concern is with the compressor. Can I run this compressor with NEMA 6-50R on a 50A breaker and heavy extension cord? Would be nice to have one plug/receptacle to deal with as thats what the welders use. Is there another receptacle/plug I should use instead? Is this a feasible idea or should I just pony up the big bucks and have it all ran through attic and plugs installed in garage?
 
To avoid these ads, REGISTER NOW!

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
Yes, the price of heavy duty welding extension cords may be more than doing the job right. Disconnect the new wiring and take the cable with you to your next home when you move if you want.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,919
Location
NJ
As stated above and the compressor needs to be hardwired.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,156
Location
SE MI
My main concern is with the compressor. Can I run this compressor with NEMA 6-50R on a 50A breaker and heavy extension cord? Would be nice to have one plug/receptacle to deal with as thats what the welders use. Is there another receptacle/plug I should use instead?
If anything, I would change out the plug for the welder to match the compressor (after checking the current draw). 6-50 is the "standard" for welders (because that it what most fab shops have installed), but not many draw anywhere near 50A. What is on the compressor right now ? You can probably use a 6-30 or 6-20 with the appropriate breaker and wire.

I use 6-20 for my 2hp portable compressor (no power in the garage). It has a 12/3 SJOOW 25' cord and I have used it with a 12/3 SJOOW 25' extension. Been doing it for years. Never an issue.

Is this a feasible idea or should I just pony up the big bucks and have it all ran through attic and plugs installed in garage?
Best solution !
 
OP
T

tlinz11x

New member
Joined
Jan 4, 2025
Messages
2
What are you going to use a 120v 30a receptacle for?

Run a subpanel with a 60a feeder, then install receptacles. 50ft of heavy gauge cords will be expensive and cumbersome
120v is for a smaller welding machine and power to CNC plasma table.
 
To avoid these ads, REGISTER NOW!

ching0n

Well-known member
Joined
Jul 21, 2016
Messages
1,496
RV and generator cords are cheap on FB. I think generator cords have both 125 & 240
 

ipgenie

Well-known member
Joined
Jan 29, 2020
Messages
561
Location
Idaho
the 30a UPS is at my shop. I dont need that kind of backup power at home


Add me to the list, I've got a 30A UPS to run my critical loads sub panel in my home. I'll eventually replace it with a real inverter and larger battery but it's served us well for a few years and was repurposed/recycled so the price was right. It's hooked to a bank of external batteries at 48V and has run for 8 hours once and 6 hours once.

It seems like I've seen a 120v 30a pressure washer before but I didn't find one with a quick Google search so I might be imagining that.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,972
Location
Central Iowa
It seems like I've seen a 120v 30a pressure washer before but I didn't find one with a quick Google search so I might be imagining that.
120 volt Hotzi pressure washers are 20 amp and one of the three things I've seen in my life that was supposed to have a 6-20R. Of course, it was for a friend so I made him a 6-20 to 6-15 adapter cord.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,012
Location
Modesto, CA
Many inverter/chargers are sold for UPS applications.

Are they really fast enough to prevent electronics from shutting down during a power interruptoon ?
this isnt one of those slapped together setups.

its an APC double conversion UPS. basically always runs off the batteries and the utility power just charges them...
 

ipgenie

Well-known member
Joined
Jan 29, 2020
Messages
561
Location
Idaho
Many inverter/chargers are sold for UPS applications.

Are they really fast enough to prevent electronics from shutting down during a power interruptoon ?



We have several UPSs at our datacenters, several very large double conversion and more that switch. A good one will switch in under 10ms and the connected loads won't know anything happened. Some cheaper ones are more like 20ms but still fast enough for a seemless transition on a desktop computer.

The one at my home is a 120v 3000w APC that was removed from production when the internal batteries failed and a larger 240v UPS replaced it. It switches fast enough that the microwave and gas range clocks don't have to be reset when the power goes out. The TV and internet stay on without interruption. It would be nice if it was a double conversion but for the price I paid it's been a good fit for it's use, even if it is kind of a slapped together setup with large external batteries. When I replace it I'll likely go with a used SMA inverter that is designed for this use. Prices are often pretty good on some of the good used stuff if you keep your eyes open.
 

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
10 milliseconds is a lifetime in electronics. Plus the smps power supply in the computer will accommodate minor sags in voltage for a period.
 