Electrical help - Garage sub panel and backup generator conflicts

dan1554

Well-known member
Joined
Aug 28, 2023
Messages
77
Hi all, I just got my shop built but now need to start thinking about adding power. I have 200 amp service and want to run a 100a sub panel.

I ran in to a problem though. A previous owner installed a generac but it looks questionable. The original service lines are spliced in to much smaller wires that run to the automatic transfer switch. There is still the 200a breaker on the main panel.

My guess is that they thought since the electric baseboard was converted to propane hydronic they thought they could get away with smaller gauge wire. I don't think this will work for a 100a sub panel though.

My plan is to get a combo ats and panel (https://www.generac.com/residential...erator-transfer-switches/automatic/rxg42sha1/) so I don't have to run the 200a wires out to the current transfer switch.

Heres the main panel with the spliced mains:
Screenshot 2024-10-20 at 2.48.16 PM.png

and the transfer switch:

Screenshot 2024-10-20 at 2.47.53 PM.png

Am I on the right track here?
 
To avoid these ads, REGISTER NOW!
OP
D

dan1554

Well-known member
Joined
Aug 28, 2023
Messages
77
Ive been looking over the NEC with plans to get a permit, and we have an electrician acquaintance coming out next weekend. I'd like to be as educated as possible so I can come in to the conversation with some knowledge. It also helps me nerd out with some window shopping for new equipment.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,881
Location
NJ
Yup, somebody screwed this up and very well too.
The ATS should have been a 200a service rated version.

I would get a new 200a xfer switch and make that the main panel. Turn your existing panel into a sub panel.

Ground rods get connected into the xfer sw. Bonding jumper also happens in xfer switch.

The "new" sub-panel gets fed with 4 conductors. Grd and neutral blocks are to be isolated from each other in sub.

The generac (Siemens) panel with built-in xfer switch is ok but limited with the number of backed up circuits it handles.

You have plenty of circuits and all wouldn't be backed up.

Please get rid of the drywall screw used as the bonding screw as you make this switch.
 

Model A Fan

Well-known member
Joined
Dec 1, 2011
Messages
1,213
Location
NW Washington
Whoa :oops::oops::oops:, that's a really nasty rat's nest. I would recommend getting professional help. I like the idea of turning this one into a sub-panel and making a new primary panel.
 
OP
D

dan1554

Well-known member
Joined
Aug 28, 2023
Messages
77
@mm08822 Thanks for the help. I too like the idea of keeping the current panel, but it could certainly use some clean up. I didn't even notice the drywall screw! Looking at whole-house transfer switches. The current transfer switch is 100A (not sure if its visible in the photo), again sitting between 200A service and a 200A breaker :sick:
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,881
Location
NJ
I can't believe they cut the heater conductors off from the cables at the point of entry. Those could have been used for new circuits in the future. Only needed a box at the other end to make safe.
 
OP
D

dan1554

Well-known member
Joined
Aug 28, 2023
Messages
77
Did some research on how to move forward and got a permit. Heres the plan:
  • Run 3x #1 XHHW and 1x #6 ground in sched 40 conduit, to run up from the home panel in to the attic then down from the soffit in to a 8' long trench and up to the garage sub panel, 100amp
  • Rewire the house panel and clean it up as much as possible. This includes temporarily disconnecting the generator (Ill get a new transfer switch and reconnect it at a later date). I also found a hot wire in the panel with damaged insulation and visible copper, to go along with that drywall screw. :oops:
  • Ensure ground and neutral are separate in the house panel. The first point of disconnect is a breaker at the street meter and its bonded there. In addition to the drywall screw, there is a bare ground connected to the neutral side. Check neutral with ammeter to verify isolation.
  • Mount a bar on the box and move the grounds there
  • Remove unused breakers. I bought a new panel cover.
Hopefully I can get this all done while the kids are away at the grandparents. Any other suggestions 'while Im in there'?
 
To avoid these ads, REGISTER NOW!
OP
D

dan1554

Well-known member
Joined
Aug 28, 2023
Messages
77
Thank you both for the advice. I looked around and found a few horror stories of the conduit settling in the ground and ripping out the wall connection. I'll see if I can get expansions on both sides.
 
OP
D

dan1554

Well-known member
Joined
Aug 28, 2023
Messages
77
Well just running the conduit is taking more time and money than I thought. So many trips to the hardware store.

Anyway, here's the attic routing. You can see it coming up through the soffit, and I need to do a little zig zag to the pipe sticking up through the drywall from the house panel. Any suggestions here to make the inspector happy? I know that technically it should have another expansion joint on the long run, would you add one?

Screenshot 2025-03-26 at 10.38.30 AM.pngScreenshot 2025-03-26 at 10.43.08 AM.png
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,285
Location
Illinois near St. Louis, Missouri
Not sure which "long run" you are referring to. The one across the attic? Since it's mostly on the warm side of the insulation I would say not required but just my guess. You need two ground rods for the garage subpanel and can put them in the trench that's open. You are also going to need to make a proper connection between the conduit from the main panel to the horizontal run. If you use a large junction box that will allow later additions of other circuits without much trouble.
 
OP
D

dan1554

Well-known member
Joined
Aug 28, 2023
Messages
77
@Innovate1 thanks for the feedback. Rough-in inspection should happen monday. Here's the final attic conduit. Don't mind the copious amounts of mouse **** - it probably adds to the r-value.

Screenshot 2025-03-27 at 9.18.47 PM.png
 
OP
D

dan1554

Well-known member
Joined
Aug 28, 2023
Messages
77
First round with the panel. Disconnected the generator and cleaned up grounds and neutrals. Also removed all the old heater circuits. Really wishing they put the main breaker on the bottom. Those aluminum mains are a lot of wire to wrestle with.

Had to call it quits today and make sure the fridge stays cold. Still need to reorganize the breakers and tidy up the hots. The bottom left corner bothers me.

Screenshot_20250329-184441~2.png
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,881
Location
NJ
Vacuum and brush out the bottom. Add KO seals to the unused knockouts to keep out the visitors.

Make sure any reds and the related blacks are on adjacent stubs (vertically) to each other
 
OP
D

dan1554

Well-known member
Joined
Aug 28, 2023
Messages
77
Thank you both! Also forgot to mention that it's an older (1980s) system and there's no ground out to the meter/first disconnect. My understanding is that I either keep the house panel bonded or run a couple hundred feet of new line with a ground to the meter. Guess which option I'm choosing 😑 hopefully the inspector is understanding.
 
OP
D

dan1554

Well-known member
Joined
Aug 28, 2023
Messages
77
Passed the rough-in. I asked the inspector to take a quick glance at the panel (after cleaning and adding knock out covers re: @mm08822) and he said there was nothing obvious that he'd fail it over. Said it looked like I did my homework.

Thanks again guys for the help, this place is a great resource thanks to you. Time to start pushing some wire.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,454
Location
Richmond, VA
Passed the rough-in. I asked the inspector to take a quick glance at the panel (after cleaning and adding knock out covers re: @mm08822) and he said there was nothing obvious that he'd fail it over. Said it looked like I did my homework.

Thanks again guys for the help, this place is a great resource thanks to you. Time to start pushing some wire.
Glad it worked well and thanks for listening to advice. That doesn't always happen
 