reposting this from the general section, since i clearly missed the labeled eleectrical section...lol


Ok, I have an older house built in the late 50's.....was built with 2 wire cloth covered "Romex"

Most of teh wires in the house have been replaced with current Romex.....


However I have a circuit of outlets and switches which are out cause of a bad nuetral and I decided to replace all the feed to the outlets and to the feed side of the switches.....

I really do not want to replace the wire from the switches to the overhead lights....what a freaking mess that would make not including the extra work involved...

I have a new feed to each location an outlet was, and where the swiches are....I am NOT replacing the original light fixtures.....

My question is can i run the grounded romex to the feed side of the switch and the two wire older "romex" to the other side to the light fixtures?

Frank
 
To avoid these ads, REGISTER NOW!

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
An answer like "Will it work? Yes, will it meet code? No, probably not..." sufficient?

Most code requires you upgrade all of the circuit at the same time. (Personally: go for it...)
 
To avoid these ads, REGISTER NOW!
OP
F

frank13

Active member
Joined
Jul 23, 2011
Messages
28
Nah, i wanna do it "right" but i really do not want to rip into any walls I dont "have" to....

If current code says from the switch to an overhead light with one bulb is ok on the two wire I am leaving it, if not, I am gonna have to replace it since I wann asell the house in five or so years.....the outlet power inputs and the switch power inputs were on a bad nuetral, so I replaced all of them, the over head lights will be a nitemare
 

VHF

Well-known member
Joined
Oct 27, 2008
Messages
420
Location
NW Wisconsin
Current code would require three wires to the light fixture--hot, neutral, and ground--but 1950s code would certainly have been OK with two wires. I think it is reasonable to replace a section of bad wire without having to re-wire the entire circuit to current code, but of course some juridictions would like you to re-wire the whole house if you change a switch plate cover!

From an electrical standpoint there is no problem with running 3-conductor to the switch and 2-conductor to the fixture. The fixture itself will not be grounded (but neither are most floor/table lamps even with today's codes!)

If you have any doubts as to the integrity of the remaining cloth-covered cable it might be a good idea to put this circuit on an arc-fault breaker. I think they are a silly requirement in new houses, but they provide some good additional safety in an older house where there is a potential for the insulation to have degraded.
 