I'm building a 4 x 4 x 6 powder coating oven in my garage. Sometime this year, if me and the realtor can agree I'll actualy build my business location, but for now I'm working out of my small, but well equipped 2 car garage. Anyways, just a general question;
I have 240v/100a single phase at the house. I'll be using 4 3100 watt elements. If my calculations are correct, that's about 52 amp draw, plus another 1.5 amps for lights/fan. Add 10% for a safety margin, then a 60 amp breaker should keep her running without burning down the house. Anybody see any problems with the rest of the house while the oven is operating...ie...lights dimming, flickering ect???


I have 240v/100a single phase at the house. I'll be using 4 3100 watt elements. If my calculations are correct, that's about 52 amp draw, plus another 1.5 amps for lights/fan. Add 10% for a safety margin, then a 60 amp breaker should keep her running without burning down the house. Anybody see any problems with the rest of the house while the oven is operating...ie...lights dimming, flickering ect???