Ok, Let me ask this simple question first before I get into more details. Installing a 60 amp subpanel in garage. we ran 2 inch PVC from house to garage over 2ft deep. The electrical pulled in a 6-3 with ground. It is a Romex type NM-B. Inspector says they cannot do that because there is a ground wire inside the jacket. Pretty sure he also said that the cable used was not meant to be run underground even in PVC. I live in Louisville Ky. electrician from very reputable company here in town says they do this all the time with no problems. So i am not sure what to do at this point. Open to easy fix suggestions.


The electrician is an idiot.

Doesnt matter how many times he has done it.

Doesn't make it any more correct...
NM has NEVER been permitted for use outdoors or underground, whether it's in conduit or not.
Now im not sure what the inspector is referring to with the ground wire but he is correct on the cable not being permitted for use underground.
Tell mr "reputable electrician" to open his code book for once and read 334.10(A)(1) and 334.(B)(4), which specifically says:
Nec 2011 334.(B)(4) said:
(B) Type NM and NMS Types NM and NMS cables shall not be used under the following conditions or in the following locations:
- (4) In wet or damp locations
There is no "easy fix" for this one....
Tell mr electrician to replace the NM-b with THWN-2 on
HIS DIME!! oh and suggest he take a code class... this is pretty basic stuff......
I'd give a heads up to the inspector as well. There's gonna be 100 some customers with ****** non-compliant installs.
Did the electrician at least isolate the neutral bar, install a ground bar and 2 ground rods at the garage?