Electrical outlet info needed?

1fastvx

Well-known member
Joined
Jun 5, 2006
Messages
141
I need to run a dedicated 20 amp outlet in my house. The run goes from one end of the house to the other which is roughly 100 feet. I am trying to find out what guage romex I need to run. I am guessing 12, but I wanted to see what you guys have to say?

Thanks,

John
 
To avoid these ads, REGISTER NOW!

OldCarGuy

Well-known member
Joined
Nov 29, 2005
Messages
2,002
Location
Ohio
If the equipment at the dedicated outlet can run efficiently at 6 volts lower than the load center, 12 AWG copper will be sufficient. Increasing the wire to 10 AWG you would still drop 4 Volts over 100 feet.

I tend to overdo things and go heaver. But with the increase price of copper today, I may think twice.

Wire-Size Voltage-Drop
 
To avoid these ads, REGISTER NOW!

Gummi Bear

Well-known member
Joined
Nov 5, 2006
Messages
524
Location
Sunset, Texas
How much load will be on the circuit (watts or amps, use Ohm's law to figure)

Voltage drop is directly related to the amount of load for a circuit of a given distance.

For a single receptacle, #12/2 should be fine. (11A or 1320 w) gives you 3.6v of drop, which is the maximum allowed.
 