1) Depth of Working Space. The depth of the working
space in the direction of live parts shall not be less than that
specified in Table 110.26(A)(1) unless the requirements of
110.26(A)(1)(a), (A)(1)(b), or (A)(1)(c) are met. Distances
shall be measured from the exposed live parts or from the
enclosure or opening if the live parts are enclosed.
(2) Width of Working Space. The width of the working
space in front of the electrical equipment shall be the width
of the equipment or 762 mm (30 in.), whichever is greater.
In all cases, the work space shall permit at least a 90 degree
opening of equipment doors or hinged panels.
(3) Height of Working Space. The work space shall be
clear and extend from the grade, floor, or platform to a height
of 2.0 m (61⁄2 ft) or the height of the equipment, whichever is
greater. Within the height requirements of this section, other
equipment that is associated with the electrical installation and
is located above or below the electrical equipment shall be
permitted to extend not more than 150 mm (6 in.) beyond the
front of the electrical equipment.
(B) Clear Spaces. Working space required by this section
shall not be used for storage. When normally enclosed live
parts are exposed for inspection or servicing, the working
space, if in a passageway or general open space, shall be
suitably guarded.