Currently, in the new house I bought, there is an existing 20AMP single terminal receptacle on its own circuit. I would like to replace that with a dual terminal 20AMP receptacle. Anybody see a problem with that? Or is there some reason it might be this way that I'm not thinking of?
 
To avoid these ads, REGISTER NOW!

Davey4000

Well-known member
Joined
Oct 31, 2006
Messages
66
Location
Jefferson, GA
Apparently the PO had a dedicated circuit for something. You can replace the single 20A receptacle with a duplex 20A receptacle. In fact you can add more 20A receptacles to the circuit if you wish…within the load capacity of a 20A circuit of course.
 
To avoid these ads, REGISTER NOW!

logical

Well-known member
Joined
Aug 31, 2005
Messages
2,447
Location
Northern fringe of the Motor City Suburbs
Sometimes a single non-GFI outlet is used in an area that would normally require GFI (Ground Fault Interupter). Codes sometimes allow a non-GFI in certain areas only if it is a single outlet and it is dedicated to a sump pump or refrigerator or something...so that nothing else can ever get plugged into the circuit. If this is in a basement, garage, outdoors or near a water supply, be sure it is GFI before you use and/or expand.
 
Last edited:

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
logical said:
Sometimes a single non-GFI outlet is used in an area that would normally require GFI (Ground Fault Interupter). Codes sometimes allow a non-GFI in certain areas only if it is a single outlet and it is dedicated to a sump pump or refrigerator or something...so that nothing else can ever get plugged into the circuit. If this is in a basement, garage, outdoors or near a water supply, be sure it is GFI before you use and/or expand.

Indeed, in garage and basement areas that normally require GFCI the code does allow dedicated single receptacles for fridges and freezers. These items can trip a GFCI and you want them to work, so the code allows for these special circumstances.

Charles
 
OP
P

Pekingman

Member
Joined
Aug 16, 2005
Messages
17
Location
Phoenix, AZ
This is indeed in a garage. I forgot though, that there are actually 2 single 20A receptacles. What I don't though, is whether they are on the same breaker or not. I will have to check that when I get home today. I have a freezer pugged into one and my Air Compressor in the other. Thanks for the insight so far.
 