Since a bunch of your guys have given me great advice in the past I figured I would pick your brain again...

So a none garage related question:

My townhome is just over a year old and the outlets in the kitchen island have slowly stopped working... They are none GFI and nothing on the breaker is tripped...

The wife called today to tell me that the outlet next to the refridgerator has stopped working as well...

So my question is can outlets go bad? Or what should I be checking to help trouble shoot if everything else on that same circuit is working fine...:confused: I haven't been home yet to look it over...

Thanks for your input guys,
 
To avoid these ads, REGISTER NOW!

bobemmerich

Well-known member
Joined
Aug 23, 2009
Messages
1,611
Location
Middletown, Ct.
Buy a voltage tester and see if they have power. Double check the breaker. Sometimes a breaker won't look tripped when it is. Make sure you flip it back and forth.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
I am not sure where you are at, but a year old dwelling in the US must have GFCI in the kitchen.

I suspect you have one tripped and it is the one that is feeding all the other outlets. Find, it reset it, and your outlets will all come back.

There is an Electrical sub group where you will get a little more focus.
 
Last edited:

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,177
Location
Durango, Co.
They are probably on a GFI circut. Look around and check all the GFI's in the house to see if one is tripped. I found a kitchen circut one time that was on the bathroom GFI.
 

jeff000

Well-known member
Joined
May 6, 2012
Messages
437
They are probably on a GFI circut. Look around and check all the GFI's in the house to see if one is tripped. I found a kitchen circut one time that was on the bathroom GFI.

Does the NEC allow that?
Up here we only need GFCI within a meter of water, like a sink. But I know down there everything has to be GFCI or AFCI.

I agree that one probably tripped causing the others to go out. But having an outlet randomly stop and not be a GFCI or the like is pretty rare, but not unheard of. I would be more worried about it being caused by something eating the wire.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
IIRCC outlets in kitchen only need to be GFCI protected if theyre within 3' of a sink. If theres no sink in the island, my bet is on "back-stabbed" outlets that have failed since the OP states the outlets failed slowly over time.

Of course the OP needs to state where theyre located but GFCIs have been required by the NEC since the late 90's...


Buy a voltage tester and see if they have power. Double check the breaker. Sometimes a breaker won't look tripped when it is. Make sure you flip it back and forth.

If other outlets on the same breaker are still working as the OP stated, that rules out the breakers.

They are probably on a GFI circut. Look around and check all the GFI's in the house to see if one is tripped. I found a kitchen circut one time that was on the bathroom GFI.


Does the NEC allow that?
Up here we only need GFCI within a meter of water, like a sink. But I know down there everything has to be GFCI or AFCI.

I agree that one probably tripped causing the others to go out. But having an outlet randomly stop and not be a GFCI or the like is pretty rare, but not unheard of. I would be more worried about it being caused by something eating the wire.

Depends on the code cycle. But baths IIRCC are suppose to have a dedicated circuit and kitchens are suppose to have 2 dedicated circuits. If the house was newer (10-15yrs old) and the kitchen only had 2 circuits total then no it isnt to code!!
 
Last edited:
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Current NEC requires kitchen outlets that serve a counter top surface or that's within 6ft of a sink's outer edge to be GFCI protected. 210.8(A)(6)&(7)
 

Mustang51js

Well-known member
Joined
Jan 24, 2014
Messages
1,734
Location
Haskell nj
More than likely back stabbed outlets like posted above,prob neutral side since that's usually what goes when back stabbed.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
wylies, I don't know if you caught the "OR". So the requirement for GFCI outlets in the kitchen is not just based on distance from a sink.

Current NEC requires kitchen outlets that serve a counter top surface OR that's within 6ft of a sink's outer edge to be GFCI protected. 210.8(A)(6)&(7)

Thx! :thumbup: i couldnt remember what the distance was and i dont have my book in front of me!
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
wylies, I don't know if you caught the "OR". So the requirement for GFCI outlets in the kitchen is not just based on distance from a sink.

Nope. I was always under the impression that a GFCI was required only if there was a sink involved. I seem to remember that previous code only called for GFCIs for a kitchen countertop IF the outlet was 6' or less from the sink....I guess I have the old code drilled into my brain.....I will have to do some research....
 