Depends on what all you're planning on running at one time. Not to mention the amp draw of all that you're running.
But you should be just fine under normal circumstances, assuming none of your appliances are energy hogs beyond what's considered normal.
Figure 30A for heat pump, 20A for compressor, 10A for fridge. That's 60A, leaving you another 60A for other stuff.
It's 1800 sq ft. Half of it will be man cave with 2 ton heat pump with a 10k back up heat. I will have numerous neon lights,fridge and pop machine. The other side will will have lights and a 30 gallon air compressor. My garage is 150 feet from the pole. I have a 200 amp panel at the pole and I was told 125 amp breaker is the biggest I'm allowed in the panel
It feeds 70 amps to another panel and it's 2 hp. Could I run 200 amp straight from the meter to a panel inside?
Your math is incorrect.......that would be 55a @ 240v
It feeds 70 amps to another panel and it's 2 hp. Could I run 200 amp straight from the meter to a panel inside?
Without a disconnect, no.
I'M CONFUSED !It feeds 70 amps to another panel and it's 2 hp.
It doesn't matter, your math is still incorrect. You can't just add up 120v and 240V amperages. That is simply not how it works.55A or 60A, not really a big difference, is it? Especially since I was just pulling numbers out of my ***, due to no specs given by the OP.
Well, maybe. In general wylie is correct.
IF the feed to the meter is rated for 400A (not typical)
and
IF your meter is designed for dual outputs
and
IF your local power company and building inspector approve it ...
I'M CONFUSED !
So you have a 200A load center (the industry standard name for a circuit breaker panel) mounted on an outside pole, presumably close to the meter. Correct?
This load center feeds another building from a 70A breaker ?
Where is your 2HP compressor currently located ? In the "other" building ?
Is there any current feed to your shop ? Code requires only one feed per building.
Unless you thinking about any new major tools like a welder or plasma cutter, I think you will be fine with a 125A feed to the shop. Worst case would be the compressor and backup heat. Feed wire size will be based on distance (i.e. voltage drop).
Good point ! I didn't think of that !!Guaranteed he will not be allowed to have a 150' section of unfused wire on the load side of a service!
It doesn't matter, your math is still incorrect. You can't just add up 120v and 240V amperages. That is simply not how it works.
It's 1800 sq ft. Half of it will be man cave with 2 ton heat pump with a 10k back up heat. I will have numerous neon lights,fridge and pop machine. The other side will will have lights and a 30 gallon air compressor. My garage is 150 feet from the pole. I have a 200 amp panel at the pole and I was told 125 amp breaker is the biggest I'm allowed in the panel
EGADS! You said man cave. You are doooomed around here.