Kind of. I've seen this argument passed around a lot, but in general when someone brings this up with the manufacturer, the response is that a breaker is acceptable. My guess is that most of where this happens is with someone doing a poor job translating the nameplate from Chinese into English, and the NRTL stamp will be questionable.
That's also because the nameplate doesn't override the instructions, which typically says fuse or HACR breaker.
So I'm yet to see an actual need for a fused disconnect for a mini-split, but I'm also not willing to say the need doesn't exist. I will say that exterior fuses are a point of failure to be avoided at all costs.
Lol
The nameplate trumps all.
It is permanently affixed to the device.
Printed manuals are mostly discarded with the lunch trash that day or its the wrong manual supplied. It's just a piece of paper.
But even if not discarded the nameplate rules.
Quick, not so quick story.
Worker goes to POCO yard to pick up a transformer to install. He knows he needs a 120/240.
There is a handmade Manila tag on the primary bushing that reads 34.5 Y/ 19.9, 120/240.
Ok cool. Here it is boys, loader up. Let's get this thing changed out so I can get to my son's BB game! Hurry up hurry up!
Transformer replaced. Woohoo. Heat'r up let's go!
Transformer energized.
Holy ****, open it up, open it up. Wtf?
So now house are smoking, people are running out saying wth is going on? My house is full of smoke!
Well , a 120/240 transformer looks the exact same externally as a 240/480 transformer,
Except for the NAMEPLATE.
Turns out the warehouseman mismarked it when doing inventory.
Lesson.
Always check the NAMEPLATE when you load it up.
Always check the NAMEPLATE when you hang it on the pole.
Always check the NAMEPLATE before you energize it.
Always and NEVER trust a written or printed document when there is a NAMEPLATE affixed to the device.
If the NAMEPLATE is wrong then that is not on you.