65cayne;1713851
Falcon said:
I believe the 100A panel is fed directly from the main lugs on the 200A panel, essentially, from the meter. I'll have to check. This would mean that the main feed from the meter would have to be upsized to account for the additional load capacity, giving me a 300A service? [/COLOR]
I can't install a 100A breaker in the 100A panel if there are already a dozen circuits in there can I?
Thanks for the input guys.
In my case, the 100A box will hold 6 breakers but I will use only one in there. If there are already circuits pulled from the 100A panel, then no - you can't really put a 100A in there. If it's close to the 200A box and there is space, those could be re-routed to the 200A box. That would be ideal IMHO, because then you could use the 100A box to be your garage overcurrent limit. Any box with a main breaker installed in the garage becomes more of a convenient local disconnect.
My PoCo did the install (for free) and they did not seem to think that a 200A house panel with a 100A shop panel on the same 4/0 aluminum feed was any big deal. So technically - yes, I can pull 300A through the meter. It's their wire, so what-me-worry.
Practically - I'd have to work at hitting 150A with the house and shop running full song on most days. I could see maybe 200A+ in the winter since our house is all electric and the house heater pulls 60A easy when all the elements are running. We'd have to have the heater, dryer, water heater and stove all running at the same time plus the shop compressor, mill, lathe, lights, well pump (drained in winter - yard only), drill press, shop heater, etc to even get close to that number.
I tested my old shop one Saturday by switching on all lights, DP, lathe, mill, heater, 3.5HP compressor and fans and I just barely got to 50A draw. I think it was 49.6 or some such - got it written down somewhere.