I'm not an electrician, although I have been known to dabble. A seriously outdated version of the NEC is a favorite bathroom reader...
My property is fed by a 100A single-phase 240VAC main panel. The source is an overhead feed supplied by a dedicated transformer on the pole out front. (i.e., it is "my" transformer, since I am the only subscriber connected to it.)
My main service panel feeds:
a. The house, which has a 100A subpanel inside.
b. A pumphouse, which is on a 20A 240VAC breaker, whose load is a small submersible pump that provides water.
c. A shed with a subpanel fed by a 50A 240VAC breaker. Loads connected to the shed include a 5HP 240VAC air compressor (something like 23A continuous when running), a 40A circuit for a welder (rearely used) and a couple of 15/20A circuits for lights and plugs.
When the compressor starts (magnetic starter), it causes a voltage drop noticable enough that the lights will dim in the house, and light loads like thermostatically-controlled box fans will actually stop.
The entire time the compressor runs, the lights in the house flicker. (mostly compact fluorescents). The fans, etc., will restart once the compressor shuts off. I haven't measured the actual voltage fluctuation, but I am ready to.
Will upgrading to a 200A main service panel help? If so, why? It seems that if the compressor is drawing enough current to max the current service, I would be tripping breakers. The feeders to the shed subpanel are #6 copper in a 35' run. The feed from the sub to the compressor is #10 copper, about 15'
Should I be more concerned about inadequate supply from the power company?
My property is fed by a 100A single-phase 240VAC main panel. The source is an overhead feed supplied by a dedicated transformer on the pole out front. (i.e., it is "my" transformer, since I am the only subscriber connected to it.)
My main service panel feeds:
a. The house, which has a 100A subpanel inside.
b. A pumphouse, which is on a 20A 240VAC breaker, whose load is a small submersible pump that provides water.
c. A shed with a subpanel fed by a 50A 240VAC breaker. Loads connected to the shed include a 5HP 240VAC air compressor (something like 23A continuous when running), a 40A circuit for a welder (rearely used) and a couple of 15/20A circuits for lights and plugs.
When the compressor starts (magnetic starter), it causes a voltage drop noticable enough that the lights will dim in the house, and light loads like thermostatically-controlled box fans will actually stop.
The entire time the compressor runs, the lights in the house flicker. (mostly compact fluorescents). The fans, etc., will restart once the compressor shuts off. I haven't measured the actual voltage fluctuation, but I am ready to.
Will upgrading to a 200A main service panel help? If so, why? It seems that if the compressor is drawing enough current to max the current service, I would be tripping breakers. The feeders to the shed subpanel are #6 copper in a 35' run. The feed from the sub to the compressor is #10 copper, about 15'
Should I be more concerned about inadequate supply from the power company?