Electrical Service to Shed

rroberts

Member
Joined
Jan 1, 2013
Messages
5
Location
Arkansas
Hey all! Need some guidance on wiring project...

I have a small shed approx 250ft from service pole. I am planning on running power from pole to shed for 30amp/240v service. I would like to bury wire in a trench inside of plastic conduit for ease of replacement or upgrate later on.

OK Now, what would be the proper wire (and cheapest) I would need to do this?

I know I will need two hot wires and a neutral but will I need to also run a ground back to the pole or will grounding at shed be sufficient?

Is THHN the best wire to use?

Also, What size conduit would be proper?

Thanks Guys
 
To avoid these ads, REGISTER NOW!

p_mori7

Well-known member
Joined
Mar 23, 2010
Messages
3,340
Location
Montreal, QC., Canada
Is the shed the only building on the property ?

Might there be another building with power closer to the shed ? That would make it easier to run power to the shed.

Total run will need to be taken into account for wire sizing.
 

Roots

Well-known member
Joined
Oct 31, 2010
Messages
1,788
You might want to contact your utility or AHJ about what their requirements are to tap into... This might not be a job which a home owner is even allowed to do.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I can tell you for 30A at 250', I would most likely pull at least #6 aluminum XHHW-2 using at least 1" PVC conduit. I'm assuming this will be a branch feed from a service panel at the pole so you will need 4 conductors. If I was running conduit thinking I may increase the power in the future I would probably use 2" PVC.

Edit: Actually #4 aluminum for 30A at 250' would be better.

*
 
Last edited:

tylernt

Well-known member
Joined
Jan 24, 2013
Messages
182
Location
Idaho, US
I believe buried conduit is considered a wet location by the NEC, hence pattenp's suggestion of XHHW instead of THHN.

Whatever size conduit you determine that you need, I'd go up a size or two from there to allow for future expansion and to make pulling easier.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I believe buried conduit is considered a wet location by the NEC, hence pattenp's suggestion of XHHW instead of THHN.

Whatever size conduit you determine that you need, I'd go up a size or two from there to allow for future expansion and to make pulling easier.

Actually most if not all THHN wire is also THWN rated which is for wet locations. I just suggested XHHW because that's common on aluminum. And conduit underground is considered a wet location.
 
To avoid these ads, REGISTER NOW!
OP
R

rroberts

Member
Joined
Jan 1, 2013
Messages
5
Location
Arkansas
Is the shed the only building on the property ?

Might there be another building with power closer to the shed ? That would make it easier to run power to the shed.

Total run will need to be taken into account for wire sizing.

I have a house but the pole would be closer.

What kind of connection will be made at the pole? Is there a meter with a breaker panel?

Yes, meter with disconnect box. I will install a outdoor subpanel to run the feed.

You might want to contact your utility or AHJ about what their requirements are to tap into... This might not be a job which a home owner is even allowed to do.

I live out in the country. It will be no problem with my electric cooperative.
 

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
Conduit size depends on what your planned upgrade will be. Installing conduit sized for the current 30A wire is worthless because you can't run anything larger in it. 100A service will require 1.5" conduit, 200A needs 2" minimum. Frankly, you might be better off just buying larger USE direct burial cable now and not using conduit. You can always run 30A on larger wire than needed (though we might need another four page thread to debate that... :wtf:) and simply increase the circuit to the max allowed amperage of the wire at a later time.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Be aware, USE type wire is not allowed by NEC to be run inside of the structure. You would need to transition to a wire type with fire retardant insulation such as THHN/THWN or RHH-RHW or XHHW in a junction box on the outside of the building.
 

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
Be aware, USE type wire is not allowed by NEC to be run inside of the structure. You would need to transition to a wire type with fire retardant insulation such as THHN/THWN or RHH-RHW or XHHW in a junction box on the outside of the building.

OK, to clarify, use USE-2/RHH/RHW-2, which is about all one can buy easily around here when you ask for USE type wire. The 2-2-2-4 version of this is readily available at Home Depot, Lowes, and others. Even electrical supply houses sell the USE-2/RHH/RHW-2 rated wire.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
OK, to clarify, use USE-2/RHH/RHW-2, which is about all one can buy easily around here when you ask for USE type wire. The 2-2-2-4 version of this is readily available at Home Depot, Lowes, and others. Even electrical supply houses sell the USE-2/RHH/RHW-2 rated wire.

The USE-2/RHH/RHW-2 that HD and Lowes sells is called Mobile Home Feeder. Lowes and HD also sell URD which is only USE-2. I've seen a fair amount of people on this site buy the URD thinking it can be run inside the building.
 

James-W

Well-known member
Joined
Feb 3, 2013
Messages
12,432
Location
Southeastern Wisconsin
I am completely confused. From reading over the posts in this thread I gather that you have a pole with a meter on it and you want to run power from the pole to the shed. Is that correct? Meters are generally mounted on the house, not on a pole, so if that is what you have it is a new one on me.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
I am completely confused. From reading over the posts in this thread I gather that you have a pole with a meter on it and you want to run power from the pole to the shed. Is that correct? Meters are generally mounted on the house, not on a pole, so if that is what you have it is a new one on me.