Electrical sub panel Sq D QO™ Plug-On Neutral Breakers

Cadmandu

Well-known member
Joined
Oct 14, 2020
Messages
56
Location
Va
I have a 200 amp Sq D QO 2003 style main panel in the house and i bought a 100 amp Sq D sub with a main for the garage.
I need a 90 amp branch breaker for the house panel. Do these old QO standard breakers in the house fit my new QO™ Plug-On Neutral sub for garage.
TIA
 
To avoid these ads, REGISTER NOW!

infinkc

Well-known member
Joined
Jan 19, 2012
Messages
862
yes the QO will fit in a plug on neutral panel and work fine. if you have arc fault/gfi breakers from the old panel, i believe you still have to connect the pigtail to the neutral bar. Plug on neutral breakers will not fit a QO panel.
 
OP
C

Cadmandu

Well-known member
Joined
Oct 14, 2020
Messages
56
Location
Va
Can I install the panle between 2x4 or do I need a piece of 3/4" plywood
 
To avoid these ads, REGISTER NOW!
OP
C

Cadmandu

Well-known member
Joined
Oct 14, 2020
Messages
56
Location
Va
What do you do with all the white nuetral wires in a sub panle if you have a plug on nuetral QO sq d panel
 

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
What do you do with all the white nuetral wires in a sub panle if you have a plug on nuetral QO sq d panel
There should still be a neutral bar with screw connections. So if talking about the connections to the breakers...
  • Regular breaker white/neutral from the wire goes to the neutral bar, hot(s) to the breaker.
  • Non-plug on CAFI, DF... (pigtailed) the neutral pigtail on the breaker needs to still go to the screw connection neutral bar, the hot(s) and neutrals from the wire go to the breaker.
  • Plug on neutral breaker gets its neutral from the plug on bus, so the hot and neutral from the wire just go to the breaker, no connection to the screw connection neutral bus.
 

cmandp

Well-known member
Joined
Dec 22, 2011
Messages
1,282
Location
New Jersey
You also would need to separate the neutral and grounds if this is a sub panel. So you need a ground bar kit, all grounds will go to that. And all neutrals will go to the neutral bar.
 
OP
C

Cadmandu

Well-known member
Joined
Oct 14, 2020
Messages
56
Location
Va
That is what I thought but that is no different than the old method except the separation of the grounds. How is the plug on nuetral breakers any faster to install
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
plug on neutral only requires the branch circuit hot and neutral wired to the breaker, where non plug on neutral GFCI breakers require an additional neutral pigtail to the neutral bus as well as the hot and neutral wired to the breaker. A regular breaker, does not have the time savings.
 

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
That is what I thought but that is no different than the old method except the separation of the grounds. How is the plug on nuetral breakers any faster to install
It is only faster (and cleaner) when using the plug on neutral breakers. If using (reusing) legacy breakers of any type there is no difference.

Here, I have also noticed that the plug on CAFI, GFCI, and DF are cheaper than the older pigtail models... not sure if that is the same in other places.
 