Electrical wiring and data lines....same conduit?

To avoid these ads, REGISTER NOW!

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
In theory yes but it is not usually considered good practice in the communications industry and you could in theory have some interference. In reality these cables are side by side in all kinds of places. To be safe you could use shielded Cat (BTW I would use 5e or 6 why run Cat5 unless you have a bunch laying around). The coax can also be triple or quad shield--most OTS coax is cheap **** with very poor shielding.

There may also be electrical code considerations because the additional cables reduce the effective size of the conduit (they take up space so you may require a larger conduit). There could also be other code considerations regarding plenum/riser spec, mixing voltage.... As far as code I cannot comment on your jurisdiction and would even have to look up mine.
 

Ironhorse

Well-known member
Joined
Sep 17, 2012
Messages
800
Can you run electrical wires and Cat5 and coaxial cable in the same 4" conduit? Its going to be a 150 ft. run.

NO!!!

You can not mix low and high voltage together...you must run in sep pipes..this way if you have a short you do not sent 230v up your cat 5 cable...I run all voltages...with my 13,200volts I concrete the pipe in place, there is no you might be able to do it...it is no and just spend the extra $40 in pipe....well worth it 10 years from now.
 
Last edited:
OP
R

R'Addiction

Well-known member
Joined
Sep 5, 2012
Messages
164
Location
Southeast Pa.
I figured that I may have problem with emi. I have enough 4" conduit to make 2 separate runs so thats the way I'm going to go. Thanks!
 

wssix99

Well-known member
Joined
Mar 2, 2011
Messages
5,156
Location
Chicago, IL
No.
My understanding of electrical code is that low voltage and high voltage cannot share a conduit.

This is true - for good reason!

It keeps the hazardous power away from the low voltage systems. Suppose there was a cut - someone could get electrocuted by plugging in a telephone or network cable. If the wires are separated, this type of thing is not possible.
 

Vinci

Well-known member
Joined
Oct 30, 2012
Messages
136
Not to highjack the thread but its ok to run Cat5 and coaxial cable in the same pipe right?
I wouldn't. I have had problems with interference from coaxial lines run next to data lines. In my situation, it was CAT6 cables supporting gigabit Ethernet connections. We would get degraded call quality on VoIP phones and inconsistent speeds on data transfers. Once the coaxial cable was disconnected, all of the problems cleared up. We no longer allow coax to be installed in the same path as copper Ethernet, as a result.
 
To avoid these ads, REGISTER NOW!

notch4u

Member
Joined
Oct 10, 2012
Messages
7
Location
Rockland, NY
nope. and in the house they can only run 6" together but they can cross perpendicular each other without issue

you dont want is HV noise on your date or any lines. my company does creston/lutron/cctv/data etc and there is a reason why you do it like that!
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,581
Location
Long Island
I wouldn't. I have had problems with interference from coaxial lines run next to data lines. In my situation, it was CAT6 cables supporting gigabit Ethernet connections. We would get degraded call quality on VoIP phones and inconsistent speeds on data transfers. Once the coaxial cable was disconnected, all of the problems cleared up. We no longer allow coax to be installed in the same path as copper Ethernet, as a result.

What sort of coax was this?
Things just work better when you use quad-shield, or at least CATV (which has dual foil shields, but only one braid).
 

Vinci

Well-known member
Joined
Oct 30, 2012
Messages
136
What sort of coax was this?
Things just work better when you use quad-shield, or at least CATV (which has dual foil shields, but only one braid).
Sorry for the slow reply. This was CATV. I don't know what specific cable it was. I am guessing that it was installed with whatever trash Comcast keeps on their trucks. That building was one of the last that got wired before anyone (me) cared to keep track of what went into the walls.
 

jweller

Well-known member
Joined
Feb 19, 2007
Messages
108
and regular phone?

Don't bother running regular phone line, just run an extra data line. You can put the phone on a data line just fine and are more likely to want the extra data line in the future. Plus with 4 pair, you can put 2 phone lines on cat5/6.
 

kossuth

Well-known member
Joined
Sep 16, 2012
Messages
1,787
One thing to keep a watch on is your length as far as the Cat5/6 goes. If you are using it for Ethernet data technically you can have a theoretical maximum run of 100 meters or 330ish feet total.... Your speeds and quality of communications as I'm sure other IT guys will attest can and will degrade according to your quality of termination and also crosstalk injected onto it from power lines, CATV, and so on. I would be half tempted to run STP cable and terminate the shield back on the house side into the ground on your house if the switch your using doesn't have a grounding plain (most don't unless you're working with highend gear like Cisco) and leaving the other end ungrounded so you have a single ground drain. This is the type of cable I would pull in your case if I was you. http://www.cableandwireshop.com/cat...ed_23-awg_4-pair_cmx_rated_stp_lan_cable.html
 

Vinci

Well-known member
Joined
Oct 30, 2012
Messages
136
Definitely keep your runs under the 100M maximum. Exceeding that, even if everything else is clean, will leave you with connection issues that you'll pound your head against a wall trying to fix.

I'll also second using ONLY CAT6 for your communications wiring, and not 4-conductor phone cable. It's far more versatile, and you can run up to 4 analog phone lines over a single piece of CAT6.
 

The Frisco Kid

Well-known member
Joined
Apr 20, 2012
Messages
645
Location
Central Texas
Definitely keep your runs under the 100M maximum. Exceeding that, even if everything else is clean, will leave you with connection issues that you'll pound your head against a wall trying to fix.

I'll also second using ONLY CAT6 for your communications wiring, and not 4-conductor phone cable. It's far more versatile, and you can run up to 4 analog phone lines over a single piece of CAT6.


Nothing to add other than I agree on running CAT5E or 6 in lieu of 2 pair phone cable.
 

FSNut01

Active member
Joined
May 25, 2012
Messages
31
You might also want to look into running fiber instead of CAT5E or CAT 6. I just ran a 200' run of 3 CAT6 TP and now wish I had thought of fiber before I ran it.
 

Vinci

Well-known member
Joined
Oct 30, 2012
Messages
136
Fiber is nice for a lot of reasons, but it makes little sense in a house. The fiber itself is cheap enough, but the equipment on each end is many times more expensive than running CAT5E/6 with no benefit.

If you needed to run an downlink to remote building on your property, then yeah, fiber is the way to go, but you're still looking at a huge jump in equipment cost.
 

pacecar

Well-known member
Joined
May 2, 2012
Messages
236
Location
bryan, tx
hey a topic I can contribute on

no, do not use the same conduit

BICSI

https://www.bicsi.org/double.aspx?l=3374

Bicsi is a group of folks that kinda help shape standards for the telecom industry

If I remember correctly min separation distance is 6 inches

and btw the main difference between cat5 and cat6 was that cat5 was 100MB for 100M and cat 6 was 1000MB for 100 meters. Cat5e came about later and was actually a standard that allowed 1000MB but only up to about 150ft

Bicsi says you can have 100meter run with two intermediate breaks(termination point like a patch panel or 110 block) and still pass the standards

and as another poster pointed out the disadvantage of fiber is the cost of the electronics associated with it
lr=single mode=long haul or long range 16 miles
sr=muti mode= short haul or short range 500m

there's more but that's what is most widely used

other things to consider
cable size vs conduit size(cat6 takes up more room and you typically never want to fill a conduit up)
http://www.midwestamericom.com/whitepapers/cabling/Conduit Fill Capacity Table.pdf

cost, if you already have cat5 or cat5e and this is a home where runs likely never exceed 100 ft I wouldn't go out and buy cat6, it should do gig

do use cat5 in place of cat3 or 4 when running phone lines, you can either wire it at the jack for phone or data, or wire it all for data and make different jumpers for the patch cable to the phones
 

Vinci

Well-known member
Joined
Oct 30, 2012
Messages
136
I suggest going with CAT6 if you have to buy cable. It costs almost the same as CAT5E, and it can handle 10-gigabit over short distances. Since that is the way things are going in the future, CAT6 offers a little more longevity.

CAT6A offers even more future proofing, as it will handle 10-gig at a full 100 meters. It is, however, close to triple the cost of CAT6.
 