I have two 27k BTU MRCOOL mini split that needs to be installed for my house. I am at SF bay area, CA.
I have two car attached garage which has subpanel and then there is main panel+meter base outside the wall.
I am pulling two 240v circuits, each on their own 40amp circuit breakers from the subpanel in garage.
First pull will be about 50ft from subpanel to first condenser disconnect and about 25ft from subpanel to second.
First condenser is on north of the house while second one is to the south. Subpanel in garage is closer to south condenser.
I plan to have sch80 pvc 3/4inch conduit from subpanel, then thru floor to the crawlspace and then to AC disconnect box.
I am planning to have 10-AWG THHN wires - Red and Black for hot and 12-AWG THHN Green for Ground.
Can I get away with 12-AWG THHN for ground or should I cough up for 10-AWG for Ground as well?
Also, given 500ft of 10-AWG cost less, can I reuse Red/Black as ground and tape/mark appropriately at panel and disconnect that its Ground?
CA is at 2022 NEC code, FWIW.
I have two car attached garage which has subpanel and then there is main panel+meter base outside the wall.
I am pulling two 240v circuits, each on their own 40amp circuit breakers from the subpanel in garage.
First pull will be about 50ft from subpanel to first condenser disconnect and about 25ft from subpanel to second.
First condenser is on north of the house while second one is to the south. Subpanel in garage is closer to south condenser.
I plan to have sch80 pvc 3/4inch conduit from subpanel, then thru floor to the crawlspace and then to AC disconnect box.
I am planning to have 10-AWG THHN wires - Red and Black for hot and 12-AWG THHN Green for Ground.
Can I get away with 12-AWG THHN for ground or should I cough up for 10-AWG for Ground as well?
Also, given 500ft of 10-AWG cost less, can I reuse Red/Black as ground and tape/mark appropriately at panel and disconnect that its Ground?
CA is at 2022 NEC code, FWIW.