The #6 wire is not in the picture because it wasnt pulled up yet but is there now.Looks bigger than #4 al. But hard to tell for sure. The white wire looks the same size as the others. Do u know what kind of cable that is? Looks like individual wires. And if thats in 1.25" conduit the conduit fill may be over capacity.
Also, cant tell if the neutral bar on the left is connected to the right neutral bar but if it is and its bonded to the can (judging by the green screw it probably), then u have another problem. Its a 4-wire feeder so the neutral bar should be isolated...I also see no GEC for grounding electrodes....
Wrong. If its protected by 100a breaker then he needs wire bigger than #2 AL. Also, at 230' voltage drop comes into play. Sure he could use #2 and deal with voltage sag....not ideal or recommended...
Also the neutral is isolated from ground.