Electricians is this a problem

23 CHIEF

Well-known member
Joined
Jul 24, 2013
Messages
150
Location
Buffalo NY
9ce77e3a039e88e6c346bf6da30f9709.jpg


When I ran my 6-3 thru the LB I got couple spots like this it like a dent it does not go thru the outer gray covering it just like it got pressed to hard in the fitting
 
To avoid these ads, REGISTER NOW!
OP
2

23 CHIEF

Well-known member
Joined
Jul 24, 2013
Messages
150
Location
Buffalo NY
OK so needs tape or no tape it's fine the way it is. Is there a way to prevent this from happining
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,582
Location
Fullerton, CA
340.24
Bending Radius. Bends in Type UF cable shall be so made that the cable is not damaged. The radius of the curve of the inner edge of any bend shall not be less than five times the diameter of the cable.

Does the LB provide for this?
It may be a better solution to use a junction box.
 