Are there any texts that reference formulas and practice for elevated slabs? Are there so many variables that only an engineering firm can calculate the design? Asking for a friend.
 
To avoid these ads, REGISTER NOW!

LopezBart

Well-known member
Joined
Oct 13, 2023
Messages
2,521
Location
Lopez Island, WA
If the slab stiffness is ignored in the floor support design, a slab like this is just a very heavy dead load and the design is not unusual and you may be able to find prescriptive solutions. Note that increasing the floor stiffness (reducing deflection) will help prevent cracking in the slab, but such cracks are difficult to avoid.

If the slab's resistance to bending is part of the design (likely along with cast in place girders and lots of rebar), you have a much more complex issue, both in design and construction, and you're looking more at commercial practice rather than residential, and engineers will definitely be involved.

Note that hydronic heating often uses poured concrete or "gypcrete" (a lightweight "concrete") for the floors, and these are not necessarily on grade. It does mean lots of girders supporting the floor - a 4" concrete slab is order 50 lbs/square foot of additional dead load. From personal experience, it does make for a quiet and solid feeling house.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,930
Location
Thousand Islands NYS
How clear do you need the space under to be? Not so hard if you can live with supports - walls and or beams - 10' or less on center. 8" formed or block walls 10: on center and steel form deck. No rebar required.

Also check out ICF floors. First on that pops up is Amdeck by Alleguard. They seem to engineer and sell whole system. No experience, just have read.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,043
Location
Northern Virginia
What size slab?

We do structural concrete slabs in garages with integral grade beams. The dirt is a one shot mold for the concrete and its loose fill. Over time, the dirt below the slab compresses and sinks away leaving the structural slab floating by its perimeter support as it was designed.

If the dirt below the slab were to be fully removed (as some folks later do by making an entrance from the basement) they create a room below the slab. Or you provide robust form work to support the concrete until it sets up.
 

wssix99

Well-known member
Joined
Mar 2, 2011
Messages
5,155
Location
Chicago, IL
Asking for a friend.
lol

Are there any texts that reference formulas and practice for elevated slabs? Are there so many variables that only an engineering firm can calculate the design?
Generally, yes. An engineer is needed to design a custom slab. Little things can turn a simple slab into a relatively complex engineering problem.

There are systems that offer pre-engineered solutions that may cover simple scenarios, like LiteDeck: https://liteform.com/products/litedeck/litedeck-steel-rib-system.html

I have personally not seen anything pre-engineered that could take the load of vehicles, so an elevated garage slab will probably need to go back to the engineers.
 
OP
O

OneEyedMan

Well-known member
Joined
Sep 4, 2015
Messages
157
Elevated Slabs for Dummies, Page 36....
Exactly. I would very much enjoy learning every detail that goes into designing a steel and concrete structure. In lieu of traveling back to my young self to sell the virtues of pursuing an engineering career, I would like some hard fast parameters.
 
OP
O

OneEyedMan

Well-known member
Joined
Sep 4, 2015
Messages
157
What size slab?

We do structural concrete slabs in garages with integral grade beams. The dirt is a one shot mold for the concrete and its loose fill. Over time, the dirt below the slab compresses and sinks away leaving the structural slab floating by its perimeter support as it was designed.

If the dirt below the slab were to be fully removed (as some folks later do by making an entrance from the basement) they create a room below the slab. Or you provide robust form work to support the concrete until it sets up.
I had looked at doing a ground formed slab by backfilling a foundation with sand and using extra rebar. A FB find of pan decking changed my outlook. Proposed project is 12’ span, 80’ length, now using pan decking on 4x6 ledger angle anchored to 8” walls. #6 rebar on 1’ grid. Not sure it’s enough, was told 6” slab would work but thinking 8”. I don’t know if extra is enough or not. Point load could justify the extra though not a driveway area.
 

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,175
Location
Durango, Co.
This is not the time for guessing. A 12’ single span with 6-8 inches of concrete and rebar is going to be pretty heavy. It will require some serious decking. You might consider beams for the 12’ span and running the decking the eighty foot way. The ledge angle can be a lighter, the decking and rebar can be lighter and make sure you are using galvanized Conform decking.
 
OP
O

OneEyedMan

Well-known member
Joined
Sep 4, 2015
Messages
157
This is not the time for guessing. A 12’ single span with 6-8 inches of concrete and rebar is going to be pretty heavy. It will require some serious decking. You might consider beams for the 12’ span and running the decking the eighty foot way. The ledge angle can be a lighter, the decking and rebar can be lighter and make sure you are using galvanized Conform decking.
Not a bad idea to rotate the orientation 90 degrees. I can get 14” H beam to span 12’. One project manager I talked to, not an engineer but the guy doing the building, said they did 8’ spans with this decking with 6” concrete and #4 bar and were good for a 10k forklift to drive on. Not engineering terms, but something to start at.
 
To avoid these ads, REGISTER NOW!

readhead

Well-known member
Joined
Dec 8, 2012
Messages
6,175
Location
Durango, Co.
Get beam height out of your head. You can span 12’ with a 10” beam if it is specified correctly. You really need to talk to an engineer for the best and most cost effective design.
Is there a permit involved for this project? If so you will probably be required to provide engineering.
 

firebirdparts

Well-known member
Joined
Jun 8, 2016
Messages
10,578
Location
Kingsport, TN
Exactly. I would very much enjoy learning every detail that goes into designing a steel and concrete structure. In lieu of traveling back to my young self to sell the virtues of pursuing an engineering career, I would like some hard fast parameters.
So first you need to pick a geometry. I don't even know if I can even list them. Like for instance:
- reinforced concrete with drop beams
- reinforced concrete without drop beams
- post tension with drop beams
- post tension without drop beams
- steel supported, red iron
- steel supported, trusses

Then, as a separate parameter, you have:
- point supported, slab continues
- point supported, slab ends
- line supported, slab continues
- line supported, slab ends

So I think, if you want rules of thumb you need to go through this and pick just one thing. then you can look for examples of that one thing and you can actually do a pretty good job of thinking about how your situation compares to the example. In my opinion, anyway. I grew up on a farm - You can do a lot just by building something stronger than necessary. That becomes VERY HARD to do with reinforced concrete. It's considered forgiving, but it's unbelievably heavy, and you've seen several fatal errors that you can probably remember.
 

firebirdparts

Well-known member
Joined
Jun 8, 2016
Messages
10,578
Location
Kingsport, TN
Here's one example, go to Walmart and look at the ceiling. That's truss supported and the slab only spans a few feet. really strong.
 

firebirdparts

Well-known member
Joined
Jun 8, 2016
Messages
10,578
Location
Kingsport, TN
Here's another example - everybody will remember this. This is not a slab, but it does show that you can convince yourself to build a pedestrian bridge 175 feet long that weighs 1000 tons. Seriously, 1000 tons. Concrete can be a very stupid choice sometimes, as it was here. they all agreed to it somehow.
 

Rusted Nut

Well-known member
Joined
Dec 11, 2022
Messages
1,802
Location
PNW
I had looked at doing a ground formed slab by backfilling a foundation with sand and using extra rebar. A FB find of pan decking changed my outlook. Proposed project is 12’ span, 80’ length, now using pan decking on 4x6 ledger angle anchored to 8” walls. #6 rebar on 1’ grid. Not sure it’s enough, was told 6” slab would work but thinking 8”. I don’t know if extra is enough or not. Point load could justify the extra though not a driveway area.
The correct gauge of pan deck will span 12’, I’ve poured lots like that; but not making an engineering judgement here. An 8” slab will be weaker than a 6” if not correctly reinforced, and you would have to reshore a 8” slab, possibly a 6” as well.. Contact a structural engineer..
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,930
Location
Thousand Islands NYS
The other option is to have concrete planks delivered. Flexicore is a kind of brand name that's become generic. Maybe more properly prestressed precast hollow core panels.
 

abfish

Active member
Joined
Sep 20, 2024
Messages
39
My company shop has a 5" thick fiber-reinforced slab. It has no cracks after ten years. We often have a dump truck or truck tractor in the shop for service.

It's like building a road- what's under the surface is as important as the surface course. Properly compacted, select fill is the key.
 

carlaisle

Well-known member
Joined
May 14, 2022
Messages
361
You haven't shared your friend's required design loads or most other pertinent information. It's a 12' by 80' project. It's not a driveway area, but does have an implied, unspecified point load concern.

An equivalent to the joist span tables that exist for lumber doesn't really exist for elevated slabs/reinforced concrete because there are too many variables. You can easily clear span 12' with reinforced concrete. The required deck thickness, beam spacing (if any), bar diameter and spacing/placement, etc. are all functions of the design requirements.

Bill's suggestion of precast flown in via crane can be very cost competitive when you add up the labor savings. And don't discount the ICF floor forms. They're a little pricey, but they save a ton of time.

If you can get your friend to cough up some more pertinent details we'll probably be able to offer some more pertinent help.
 

rharman

Well-known member
Joined
Apr 22, 2012
Messages
8,737
Location
SoCal
When I hear "elevated slab", I'm envisioning an open, usable space underneath. Is that correct?

If that's the case, does your "friend" really want his wife, kids, or anyone, underneath that thing without it being professionally designed/engineered and constructed?

Maybe I'm misunderstanding the premise but this just screams "DUMB IDEA".
 

reader2580

Well-known member
Joined
Dec 31, 2014
Messages
14,515
Location
Minneapolis, MN
Pre-stressed concrete is commonly used for garage floors with a room underneath. No idea on the cost. My parents bought a two year old house in 1981 with a garage like this that has another garage underneath. My father made the space into a shop along with an area to store all the lawn and garden stuff.

If you do this make sure a rubber membrane is laid over the pre-stressed concrete before the concrete cover layer is added. My parents didn’t have this and water got into the space below. A few years ago they had the finish layer of concrete removed and a membrane add with new concrete finish layer. It cost over $20,000 to fix.
 
To avoid these ads, REGISTER NOW!