EMT?

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
The panel is flush mounted. Can I just fire in an "LB" 6" above the panel, let's say a foot above, and pull the wire through the wall into the panel?

No. All conductors need to be enclosed in a raceway ( conduit) or be part of an approved cable assembly ( NM-B or MC ) for their entire length from panel to box or fitting.
 
To avoid these ads, REGISTER NOW!
OP
S

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,771
Location
AK
No. All conductors need to be enclosed in a raceway ( conduit) or be part of an approved cable assembly ( NM-B or MC ) for their entire length from panel to box or fitting.
So how is it done? Seems crazy to patch in 3 feet of romex for no reason aside from the 1/16" added wrap it has over THHN
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
The stuff I already have came from an old job wiring a shop (was leftovers the electrickcans left behind) and it's stranded wire. That better or worse?
I have I think 2 500ft spools of red and black in 12 guage and a spool of green, but I can't remember for sure.
Your going to need a roll of white as the NEC does not permit taping individual conductors smaller then 4 AWG white or green.
 

kaffine

Well-known member
Joined
Dec 13, 2009
Messages
3,610
Location
Henderson, NV
I expect to need a fair bit more than 200 ft. 1/2" can fit 9 12 gauge wires or 12 14 gauge

The stuff I already have came from an old job wiring a shop (was leftovers the electrickcans left behind) and it's stranded wire. That better or worse?


I also need to remember that this is electrical conduit not communications conduit. Less likely to pull in another cable in electrical conduit. I'm currently redoing my entire house with conduit. I'll see how far I make it using 3/4". Trying to use EMT for everything except the under slab portion.

Stranded wire is easier to pull. I only use back wire devices with the screw clamps so terminating it is easy. It is a bit harder to terminate stranded if using side wire wrapping it around the screw. I wish they would make stranded 12 gauge NM cable as I hate using solid wire.
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
So how is it done? Seems crazy to patch in 3 feet of romex for no reason aside from the 1/16" added wrap it has over THHN

The easiest way is to fish in a section of flexible metallic conduit ( greenfield ) from your LB to the panel. Pull your conductors through this raceway.

It's not crazy to follow the NEC. The NEC doesn't allow individual conductors to be run indoors without a raceway or as part of a listed cable assembly.

Steve
 
OP
S

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,771
Location
AK
The easiest way is to fish in a section of flexible metallic conduit ( greenfield ) from your LB to the panel. Pull your conductors through this raceway.

It's not crazy to follow the NEC. The NEC doesn't allow individual conductors to be run indoors without a raceway or as part of a listed cable assembly.

Steve
It's crazy to follow codes blindly. I understand MOST, but this one has me wondering.

What reason would there be that Romex is fine inside a wall but individual wires aren't.

I could probably cut the OSB above and below the panel if need be.
 
Last edited:

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,977
Location
Richmond, VA
It's crazy to follow codes blindly. What reason would there be that Romex is fine inside a wall but individual wires aren't.
You can understand the code or not, it doesn't matter. It isn't a guideline, it's a rule. Break it if you want, but there may be consequences. Anything from a failed inspection, to a denied insurance claim
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
It's crazy to follow codes blindly. What reason would there be that Romex is fine inside a wall but individual wires aren't.
It's even crazier to decide that your smarter then the ones writing the code, most of what is required is there for good reason, with the exception of AFCI's.
You can understand the code or not, it doesn't matter. It isn't a guideline, it's a rule. Break it if you want, but there may be consequences. Anything from a failed inspection, to a denied insurance claim
Everyone keeps bringing up denied insurance claims, not ever heard that being done, still not a excuse to do crappy work though, do it right or not at all.
 

racecougar

Well-known member
Joined
Jan 26, 2021
Messages
5,190
Location
Missouri
It's crazy to follow codes blindly. I understand MOST, but this one has me wondering.

What reason would there be that Romex is fine inside a wall but individual wires aren't.

I could probably cut the OSB above and below the panel if need be.
The sheathing on NM-B provides physical protection that THHN lacks.
 
OP
S

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,771
Location
AK
The sheathing on NM-B provides physical protection that THHN lacks.
I don't think the not even 1/16" outer insulation of Romex would do a whole lot that the insulation of THHN wouldn't? Only thing that would maybe happen in a wall cavity is a nail or screw, or I guess if you have a horrible mouse infestation, mickey and his buddies gnawing on it.
 

racecougar

Well-known member
Joined
Jan 26, 2021
Messages
5,190
Location
Missouri
I don't think the not even 1/16" outer insulation of Romex would do a whole lot that the insulation of THHN wouldn't? Only thing that would maybe happen in a wall cavity is a nail or screw, or I guess if you have a horrible mouse infestation, mickey and his buddies gnawing on it.
The point is that it is a second layer of protection, intended for physical protection rather than electrical isolation. You can think what you like, but there is a reason why the code states what it does.
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
Do they still make these that have knock outs on all sides with a lid on the front? We have them at work on installs, but I have no idea what they are called, if there are still a thing even.


Just use a 4" square x 2 1/8" deep metal Jbox. It has knockouts on all 5 sides. Than slap a blank metal cover on it. Easy
 
OP
S

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,771
Location
AK
Just use a 4" square x 2 1/8" deep metal Jbox. It has knockouts on all 5 sides. Than slap a blank metal cover on it. Easy
I will have probably 8-10 conduits feeding out of it though. I doubt that would have enough room?
 
To avoid these ads, REGISTER NOW!

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
Use several 4 11/16" x 2 1/8" deep boxes nippled together then.

I haven't really seen a "wireway" like you descibed, with factory knockouts on all sides
 
OP
S

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,771
Location
AK
They make nice grey ones of various sizes. I'll have to check with the electrical supply on what they have. I can put punch my own holes in if need be.
I think for my couple time use a hole saw would work just fine?
 

RichieP_MechE

Well-known member
Joined
Jun 23, 2021
Messages
183
Location
Near Pittsburgh

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,031
Location
Central Iowa
Do they still make these that have knock outs on all sides with a lid on the front? We have them at work on installs, but I have no idea what they are called, if there are still a thing even.

They make them, a 6X6X24 is a little excessive, You'd be fine with a 4X4X12 or 4X4X24. I thought there was a 4X4X18, but can't find them on the website for the supply house I use.
I don't think the not even 1/16" outer insulation of Romex would do a whole lot that the insulation of THHN wouldn't? Only thing that would maybe happen in a wall cavity is a nail or screw, or I guess if you have a horrible mouse infestation, mickey and his buddies gnawing on it.
It doesn't matter what you think, it's not right.
They make nice grey ones of various sizes. I'll have to check with the electrical supply on what they have. I can put punch my own holes in if need be.
I think for my couple time use a hole saw would work just fine?
7/8" hole saw for 1/2" knockouts, 1-1/8" for 3/4" KO's, and if you venture into 1" conduit, it needs a 1-3/8" hole.
 
OP
S

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,771
Location
AK
They make them, a 6X6X24 is a little excessive, You'd be fine with a 4X4X12 or 4X4X24. I thought there was a 4X4X18, but can't find them on the website for the supply house I use.

It doesn't matter what you think, it's not right.

7/8" hole saw for 1/2" knockouts, 1-1/8" for 3/4" KO's, and if you venture into 1" conduit, it needs a 1-3/8" hole.
Any idea what the box fill limit is for those or where I could find it without spending $500 or whatever on the NEC book?

Wasn't arguing it wasn't a thing with no THHN in a stud bay, just I'd like to know the why and not get "because" as an answer.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,977
Location
Richmond, VA
Any idea what the box fill limit is for those or where I could find it without spending $500 or whatever on the NEC book?

Wasn't arguing it wasn't a thing with no THHN in a stud bay, just I'd like to know the why and not get "because" as an answer.
The code book doesn't give a why. It just says what you can do
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,031
Location
Central Iowa
Any idea what the box fill limit is for those or where I could find it without spending $500 or whatever on the NEC book?

Wasn't arguing it wasn't a thing with no THHN in a stud bay, just I'd like to know the why and not get "because" as an answer.
You'll be fine with box fill, especially if you use the 24" wide trough.
I actually looked for a code article stating THHN/THWN has to be in some type of conduit, but didn't come up with anything. It's there though.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,911
You'll be fine with box fill, especially if you use the 24" widChae trough.
I actually looked for a code article stating THHN/THWN has to be in some type of conduit, but didn't come up with anything. It's there though.
Article 300 has some verbiage that says 'single conductors listed in table <whatever> shall only be installed in a recognized wiring method of chapter 3'. loose single conductors isn't a recognized method (except for some outside aerial uses), so it's prohibited.
 

racecougar

Well-known member
Joined
Jan 26, 2021
Messages
5,190
Location
Missouri
Wasn't arguing it wasn't a thing with no THHN in a stud bay, just I'd like to know the why and not get "because" as an answer.
Post #52:
 
OP
S

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,771
Location
AK
Post #52:
Post #65 explained it.
 