ENT (aka Smurf)

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,978
Location
Thousand Islands NYS
Thinking about some electric in new patio (pour scheduled October 8) and was considering smurf. Never worked with it before - plenty of rigid and EMT - so was wondering if it was particularly difficult (other than sourcing in the north). Am considering 4 flush "floor" (slab?) boxes. Much less expensive than pvc and many fewer connections. Thoughts? Thank you.
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,079
Location
Central Iowa
I've only used it a couple of times, but found it to be a pain to work with. Mostly because of the pre-formed circle that it comes in. I'm sure that with enough practice it would become easier, I'm just not interested in practicing with it.
 

ycgoat

Well-known member
Joined
Mar 28, 2020
Messages
971
Location
S.E. Va
It has specific requirements, so make sure you can use it as intended. I used it make the steel cable across my property drive visible. It has worked very well
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,079
Location
Central Iowa
Lots of zip ties should make it pretty easy to control.

Admittedly, I would likely do this with pvc and a heat bender. Eliminating all the pre-made bends saves money and makes the run easier
Actually, the factory 90's are pretty reasonable. I just finished a job with 3/4" PVC. Sch 40 was $12 a stick, sch. 80 was $23, but 90's were only $1.05, and couplings were $.25. I thought that was too cheap to screw around making my own even though I have a hotbox and heating blankets. On the other hand, if for some reason I have to use 1/2", I make my own. Factory 90's are too tight and hard to get a fish tape through. That's only in extreme circumstances, I try to avoid 1/2" PVC at all times.

Without seeing this job, I'd probably be leaning towards PVC here too.
 
OP
B

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,978
Location
Thousand Islands NYS
Thank you. For a number of reasons - including not enough concrete cover for boxes and not enough planning for this - I'm going to drop it. I have building on 2 sides and partially on a third - very irregular shape - so can get power to perimeter. If I could find an acceptable exterior "tombstone" for a receptacle on the long side, I might put in one PVC run.
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
Be sure to secure the ENT at couplings and connectors very well. I had more than one come apart on me during the pour. Use plenty of tie-wire to secure the connections to the rebar.
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
I thought the Smurf was attractive because of no couplings, just connectors at device.

ENT comes in both 10' sticks and 25', 50' and 100' rolls

You may also have a short section left over that you may want to couple onto another piece.

Secondly, damage may occur during construction, where you will have to splice in a new piece before the pour
 