Evaluating a shop panel

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,126
Location
Amarillo,TX and Stinnett,TX
This is the shop panel in the shop I'm buying this week. The disconnect on the pole is 200 amps. This looks like a mess and mounted up side down?:confused:
 

Attachments

  • 20190727_125110.jpg
    20190727_125110.jpg
    87.5 KB · Views: 226
  • 20190720_113354.jpg
    20190720_113354.jpg
    100.6 KB · Views: 160
  • 20190720_113404.jpg
    20190720_113404.jpg
    39.5 KB · Views: 128
To avoid these ads, REGISTER NOW!

astroracer

Well-known member
Joined
Jun 22, 2005
Messages
3,001
Location
Mid_Michigan
No inspection prior to sale? If it's not to code it should be fixed before the sale can go thru.
Get an estimate to have it rewired correctly and deduct that from purchase price?
Mark
 

sreeb

Well-known member
Joined
Jul 29, 2009
Messages
460
Location
SoCal
Upside down is probably fine. If you have the cover, there should be information on the inside of the door. If you don't you will be replacing the box anyway.

Is the disconnect fused? If so, what size fuses?

Here in CA, you couldn't just poke the wires through the knockouts, and need to secure the wires. Running wire in front of the 2x4 in an exposed location would be a problem.

But you live in TX with less burdensome regulation so maybe it is OK there? :lol_hitti

I think you suspect that you will be replacing that box and you are probably right.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,929
Location
NW Iowa
Looks like mess. I'd be going though ALL the electrical devices in the building. If that's what the panel looks like the rest can't be much better.
 

tarmy

Well-known member
Joined
May 28, 2014
Messages
4,782
Location
Nor Cal
There is so many things wrong with that panel...that planning on starting over would be my plan...Hell, that panel frame not being hot already is amazing...
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
There is no upside or downside to the panel. It's just an installers preference as to how it's hung. With the feed coming in from the bottom it would have made a cleaner install to be turned with the main lugs to the bottom and not have the large cables running in the gutters. But the up or down is the least troubling of the issues with that panel install.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,274
Location
Modesto, CA
OMGosh what a mess :shocking:

The feeder wires arent in conduit.

No cable connectors on the knockouts

No main breaker even though theres more than 6 handles

Cordage used as building wire

Is the neutral bar bonded?

Are there grounding electrodes?

The branch circuits are surely a mess as well.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,316
Location
NJ
40'x80' shop, 4 acres and a old house $56K.

Seems like shop has much of the wiring exposed for easy inspection/rework. You may be able to salvage most electrical materials and re-install everything properly.

How bad is the house?
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,126
Location
Amarillo,TX and Stinnett,TX
I saved just under $30K from their asking price. This was a year of watching and waiting. One 200 amp service goes to the shop and I have another spare 200 amp on the same pole going nowhere(old mobile home). The old house has a meter also, not sure its size yet.
 
Last edited: