Time to start finishing the rest of the wall and ceiling in the shop...34'x40' with a 20' eve height. Once I close in the ceiling with 2x6 sleepers and OSB and 12" insulation batts, I will lose the soffet and ridge ventilation.
So I am thinking, a exhaust fan mounted high on the wall, with shutters to keep the heat in during the winter, and a variable speed control should do it. I would probably need to size out the fan fairly quickly so I would start finishing the walls.
20x34x40 would be 27,200 cubic feet, and if you figure 5 air changes an hour, 136,000 cubic of air/hour or a fan rated in 2267 cfm. This would also require panels with shutters on the opposite end of the building for make up air.
This will allow me to run a vehicle inside with the fan on or have plenty of ventilation for painting or welding.
Does anyone have a favorite supplier of fans and shutters?