Exhaust fans

Rich24

Member
Joined
Nov 15, 2012
Messages
8
I recent built a 30 by 50 pole barn with a full second floor. The upstairs will be an office/living space and I'm concerned about exhaust fumes when starting up trucks in the morning to let them warm up if someone is upstairs. Has anyone installed exhaust fans in there garages? Or is this just ridiculous?
 
To avoid these ads, REGISTER NOW!

dave67fd

Well-known member
Joined
Apr 25, 2011
Messages
872
Location
Southern NH
What kind of opening do you have to the upstairs?
Will it always be open or do you plan to seal (insulate/sheetrock etc..) it off at some point?

Most people will open the doors before they start their vehicle to minimize but for that size garage you will need some serious CFM if you want to clear it quickly. You will have to hang around and wait to shut the fan off or you could put on a timer. In cold weather it might tend to **** out your upstairs heat if it isin't sealed off well.
 

philjafo

Well-known member
Joined
Aug 31, 2012
Messages
244
I service the HVAC equipment at a county rescue, they have about a dozen ambulances in the garage and they hook up a vent right to the exhaust pipe. It's held in place with a magnet and its on a track it follows the truck till it exits. I'm not sure on the brand or a whole lot of anything about it, I service the heaters in the shop not the exhaust sucker, but I'm sure google can find you something.
 

BreeStephany

ALLIANCE MEMBER
Joined
May 19, 2012
Messages
851
Location
Oregon
They are a bit on the more expensive side, but I have set up a few shops and garages which have a series of inlet and outlet powered louvers which are controlled by a CO sensor or set of CO sensors in the shop.

Once the CO level gets above a preset level, the louvers open up and turn on exhaust fans, once it drops below a lower preset level, the louvers close and the exhaust fans turn off.

For a shop that was 80 x 140, we had 4 48" x 48" louvers on either side of the shop... I I imagine 4 36" louvers w/ exhaust fans would be sufficient for the purpose of your shop, though it would definitely be more expensive than just hooking up exhaust vents.
 
OP
R

Rich24

Member
Joined
Nov 15, 2012
Messages
8
Thanks for the ideas guys. Dave, i will start by saying that the garage you built is pretty amazing. Very nice. The second floor in my shop is has open joists right now, I have thought about insulating and doing a ceiling mainly to help with noise. Maybe that would help seal out the fumes? I have a similar set up with stairs that go to a landing in the back corner then a 90 and up to the second floor. My plan was to frame in the opening upstairs with a door to seal it off from the shop.

P.s garage doors are coming today! Feel like I have been waiting forever
 
To avoid these ads, REGISTER NOW!

DPelletier

Well-known member
Joined
Oct 23, 2012
Messages
170
OK,

first off, you need to ensure that your residential space is completely sealed off from the shop/garage and you should have an automatic closure on the outside rated connecting door. There should also be a fire rating between

Next; you shouldn't run your vehicles inside the garage (or any enclosed space) unless you have a CO removal system. Such a system can be a general exhaust fan coupled with a CO monitor drawing air from an intake louvre with a backdraft damper (fan needs to be sized to ensure adequate ventilation - ASHRAE minimum for a repair shop is 1CFM per sq. ft.) OR you can use a fancy source CO extraction system such as the Nederman hose reel systems we install in many repair shops or maintenance bays. http://www.nederman.com/products/exhaust-extraction/vehicle-exhaust-extraction/865-exhaust-hose-reel

2 cents,
Dave
 

pseudorealityx

Well-known member
Joined
Nov 10, 2009
Messages
999
Location
USA
IMC states 1.5 cfm/sq ft for automotive repair shops. That's for a commercial application, and not meant for fume removal, but general ventilation.
 