I am installing an exhaust hood with a remote blower. There is a 6 wire harness between the blower and the hood.

1 ground
1 neutral
4 power (one for each speed)

I need to provide the wires between the hood and the blower. The blower has a junction box and the hood has a provided harness connection where I'll need to nut onto the romex inside a box.

I was going to use 2 separate NM wires. One 14-2 and One 14-3. The wires will be enclosed behind drywall and and sheetmetal.

Do I need to put it into flex conduit? My fallback was to use smurf tube.

Rather than buying THHN, can I strip the romex sheath off the wires and then put them into the conduit?
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
I am installing an exhaust hood with a remote blower. There is a 6 wire harness between the blower and the hood.

1 ground
1 neutral
4 power (one for each speed)

I need to provide the wires between the hood and the blower. The blower has a junction box and the hood has a provided harness connection where I'll need to nut onto the romex inside a box.

I was going to use 2 separate NM wires. One 14-2 and One 14-3. The wires will be enclosed behind drywall and and sheetmetal.

Do I need to put it into flex conduit? My fallback was to use smurf tube.

Rather than buying THHN, can I strip the romex sheath off the wires and then put them into the conduit?


Use flex, & the conductors from NM cable cannot be used outside of the sheathing they become scrap metal if stripped out, as the conductors are not marked.
 
To avoid these ads, REGISTER NOW!
OP
S

sands35

Well-known member
Joined
May 29, 2012
Messages
936
Location
St. Joseph, MI
OK - thanks.

Looks like one 14-2 and one 14-3 will exceed fill for a 3/4" flex. I need some THWN anyway....

Am I *required* to use flex? I can get everything buried behind drywall so there isn't an issue with inadvertent contact.
 
Last edited:

VHF

Well-known member
Joined
Oct 27, 2008
Messages
420
Location
NW Wisconsin
You need some kind of conduit, flex or otherwise. You are not permitted to run THHN/THWN wires in the wall by themselves. Smurf tube should be OK.
 