I am putting in a Fe75 Rezor. Power vent exhaust. Plan is to bring the exhaust up vertically 10 ft and then thru the wall. Total of the horizontal run from the vertical is 3 ft to the cap outside. Here is the vent information from the manual.
2. Vent Pipe
If installed with a horizontal vent run, use either vent pipe ap-
proved for a Category III heater or appropriately sealed 26-gauge
galvanized steel or equivalent single-wall pipe.
If at least half of the equivalent length of the vent system is verti-
cal, vent pipe approved for a Category I heater may be used.
Single-wall pipe or double-wall (Type B) vent pipe are suitable for
use with a Category I heater.
Use only one of the flue pipe diameters listed in the Vent Length
Tables for the furnace size being installed.
So can I use B vent or must I use type iii since more than half is vertical or am I reading this wrong...Thanks