Expansion device: Capillary vs. TXV

greg_mustang

Member
Joined
May 13, 2021
Messages
10
Location
Montreal
Hi,

Most split systems i have installed in my home have been with TXV.
Recently I have had the 'pleasure' of installing a cheap unit that uses a capillary as the throttling device for refrigerant expansion.
On this specific unit, I noticed that if the refrigerant is low, the output of the capillary freezes up, blocks, and causes the suction/discharge line to go all the way into vacuum.
On my other units, which had TXV, whether related or not, though I have had cases of low refrigerant, i never experienced the discharge freezing up causing negative pressure at liquid line.

Any comments? Is this really related to the capillary, and it is normal/common in your opinion?

I am not an hvac tech, just an engineer who likes to tinker. I absolutely always respect refrigerant handling.

Thanks,
Greg
 
To avoid these ads, REGISTER NOW!

firebirdparts

Well-known member
Joined
Jun 8, 2016
Messages
10,681
Location
Kingsport, TN
Freezups on low Freon (or while heating) have always been normal here in the US on capillary equipped heat pumps. I don't know if they are harder to do with TVX, but it seems like they would be. I'm also just an engineer that likes to tinker.
 

elderstarr

Well-known member
Joined
Apr 7, 2011
Messages
98
Freezing at the expansion device can be a sign of moisture in the refrigerant. Happens with a TXV or orifice.

Was there a filter drier installed?

Never seen a system freeze the expansion device closed due to low refrigerant. Refrigerant doesn't freeze. Likely something is contaminated in the system.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Does the cap tube itself freeze, or just the evaporator at the cap tube exit?

Tommy
 
Last edited:
To avoid these ads, REGISTER NOW!

karoc

Well-known member
Joined
Dec 19, 2017
Messages
2,018
Location
Hemphill Tx
Pic would be nice of that area and I am asking for a reason, guessing this is a new system and a vacuum was pulled?
 
OP
G

greg_mustang

Member
Joined
May 13, 2021
Messages
10
Location
Montreal
Mini-split.
The expansion/throttling is done at the exterior unit, not at the evaporator.
When the refrigerant is low, the liquid line evaporates (if thats the correct term) too soon in the cycle, i.e. exactly at the output of the capillary, causing it to freeze up.
As refrigerant is added, the evaporation moves upstream into the lineset and before the evaporator, where it should be.
Hope this clarifies my hypothesis and understanding. If someone disagrees please let me know!
Thanks
Greg
Montreal - Canada
(Yes, up here too it gets hot as hell during some weeks of the summer, needing A/C).
 

mcbane

Well-known member
Joined
Jul 23, 2017
Messages
794
Location
California
Mini-split.
The expansion/throttling is done at the exterior unit, not at the evaporator.
When the refrigerant is low, the liquid line evaporates (if thats the correct term) too soon in the cycle, i.e. exactly at the output of the capillary, causing it to freeze up.
As refrigerant is added, the evaporation moves upstream into the lineset and before the evaporator, where it should be.
Hope this clarifies my hypothesis and understanding. If someone disagrees please let me know!
Thanks
Greg