Explaining NEC sec 210.11 (C)(3)

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
I have a MWBC going into the mas bath which now sits gutted out for a remodel. My plan is to use one 20A circuit for all outlets (4), 4 recessed lights and a fan all protected by a GFCI. The 2nd circuit will not power any outlets within the bathroom but will power a couple more light fixtures as well as an exterior light and outlet. I plan on using the GFCI on that exterior outlet as there will be no outlets on that circuit within the bath.

The only reason for having any lights on the 2nd circuit and even coming into the bath is if the GFCI pops at night and the place goes dark. Reading the NEC I see that this might comply because (a) you are allowed to power other devices off one 20A circuit but that power cannot leave that bathroom, and (b) you can power outlets in other bathrooms as long as the circuit is powering outlets only. I think I can have power on the lights and exterior devices because there are no bathroom outlets involved. I think the word used in the text is 'receptacle'.

The way it was previously wired was not compliant IMO. I would like to be compliant.

I don't have a 2014 book and we're still on 2011 AFAIK.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
CA is on the 2011 NEC, the 20A circuit can only serve the lights, & receptacles in that bathroom, nothing outside the bath, doesn't apply in your case but if it was just receptacles it could serve other bathroom receptacles.
 
OP
Z

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
CA is on the 2011 NEC, the 20A circuit can only serve the lights, & receptacles in that bathroom, nothing outside the bath, doesn't apply in your case but if it was just receptacles it could serve other bathroom receptacles.

I said that myself. What's new? There are 2 circuits available, did you get that part? One complies in that it doesn't go beyond the bath. The other one is the one in question: I'm wanting to use a general purpose circuit to power 2 lights in that bath.

Maybe that makes it more clear.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,796
Since you have a 20A circuit that is compliant I see no issues with another circuit being used there.
 