I want to install some extra lights in my shop. Currently there is about 500 watts of T8s installed on the ceiling. The wiring for the lights is exposed on the ceiling. Most of it is inside EMT, but there's a peice of bare romex going from the junction box to each light. (see pic)

Is it ok to have romex exposed like that? Or does it need to be inside some kind of conduit?

Basically I want to install more lights the same way...I'm just wondering if that is right or not?
 

Attachments

  • romex.jpg
    romex.jpg
    86.4 KB · Views: 490
To avoid these ads, REGISTER NOW!

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
Seems fine up there. Nothing is going to damage it. But, this is one of those interpretive things whether a wire needs physical protection.
 
OP
S

StaggeringGoat

Well-known member
Joined
Jul 1, 2011
Messages
758
Location
Oregon
So the NEC doesn't specifically say? In my opinion it's perfectly safe, just not sure if it would pass an inspection.
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
The NEC states that it must be protected from physical damage where subject to physical damage, or something close to that. Whether it is subject to damage is a matter of opinion. The NEC makes exactly the same statement for MC cable that everyone seems to think is OK on the ceiling. The problem is that some people for some reason they can't explain think MC cable is OK but romex is not. I even bought MC cable to put through trusses exposed to avoid any problems with opinions.
 

wolflrv

Well-known member
Joined
Jun 7, 2011
Messages
304
Location
Savannah, TN
My whole shop is exposed romex like that strung across the tops of the rafters. According to my buddy that did the install for me, as long as they have those white anchor pins, it's fine. Shop was arbitrarily inspected a couple of years later by a nosy inspector who was out inspecting some other work being done and the whole job passed with flying colors. I'd say you're fine with it.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
I think you are OK, as the purlin (or whatever that piece is...) protects the wire from damage from below. If the wire was simply laid out on the ceiling, it would have to be protected, usually 1x2s are put on each side of the wire.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
That definitely looks like a homeowner job!

If a guy is going to take the time to pipe across the ceiling, I'd at least use MC cable from the box to the light. That Romex looks like ****.

But, the best way would of been to stub a pipe into the ends of each light right out of the box and then eliminate the splices in the box.
 
Last edited:

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
Up here,any NMD below 1.5m(5ish')needs to be protected.It may not look the best,but would conform.
 
OP
S

StaggeringGoat

Well-known member
Joined
Jul 1, 2011
Messages
758
Location
Oregon
but it looks like someone tried to add lights after the fact, and didn't have a clue how except to run the romex.

I think that's what happened. There are other junction boxes in the ceiling where there are no lights but it looks like there should be. Whoever did the lights didn't do the EMT. Not a "homeowner" job though, this is part of a multi-million dollar shop condo complex.

My place was originally planned to have a spray booth, but then the city wouldn't allow that last minute. They did install an explosion proof heater though and probably were planning for explosion proof lighting that never happened.
 

Grazz256

Active member
Joined
Jul 23, 2011
Messages
42
Why not pipe it? It looks like a straight run for the box to the light, and it will look 50x better.

On a side note, you wouldn't use romex in conduit (I believe its even against code), you run 3 single conductors.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
For Romex in a conduit, you should ask your local building inspector, they will probably allow it for your particular case (short run, dedicated circuit).
 

cowboyjosh

Well-known member
Joined
Mar 11, 2010
Messages
1,066
Local AHJ inspectors would call you out on exposed Romex around here (CO). Also down the road when you sell a ******* Home Inspector will wet his pants and jump up and down when he spots the eposed Romex, he will definately write it up as a deficiency and want a license to repair it.
 

sdowney717

Well-known member
Joined
Mar 17, 2010
Messages
964
they would not like it here in Newport News Va.
I wonder though being way up there nothing is going to harm it.
I was told flat out no exposed romex in a garage.
Yet they have no problem if it is behind thin weak sheetrock because it is more protected from something jabbing it.
Guess what, still posting so I have not electrocuted myself yet, or maybe I am thick skinned.
 

MoonRise

Well-known member
Joined
Nov 5, 2010
Messages
4,034
Location
NJ
Ummm, commercial/shop use codes usually do not even allow Romex (more correctly called NM or NM-B).

YMMV and your electrical codes may be different.

Also, in almost every locale in the US, there is no resident homeowner exemption for doing 'commercial' electrical work. ALL commercial/industial/shop/apartment/etc work is supposed to be done by licensed electricians, not the owner/occupant. Again, YMMV (but I doubt it).
 
To avoid these ads, REGISTER NOW!

eriksalo

Well-known member
Joined
Nov 29, 2007
Messages
184
Location
Colorado
This is a difficult problem. I don't think it would pass inspection, however in practice I'll bet it's perfectly safe.

There is also a potential problem with putting Romex in conduit. That's not allowed outside or underground and opinions vary as to the legality of doing it inside.

I believe the only truly code compliant way to do this is to put individual wires in EMT.
 
OP
S

StaggeringGoat

Well-known member
Joined
Jul 1, 2011
Messages
758
Location
Oregon
Also, in almost every locale in the US, there is no resident homeowner exemption for doing 'commercial' electrical work. ALL commercial/industial/shop/apartment/etc work is supposed to be done by licensed electricians, not the owner/occupant. Again, YMMV (but I doubt it).

I have a handfull of electrical projects that I plan on doing and then getting a cheap electrician to do the final hookup, inspection, and get the permits. I'm only doing that because the owner's unit is next door and he'll see the lights...

It would take me longer to explain to an electrician what I want done and exactly how, and then check his work, than it would to just do it myself. :lol_hitti
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I have a handfull of electrical projects that I plan on doing and then getting a cheap electrician to do the final hookup, inspection, and get the permits. I'm only doing that because the owner's unit is next door and he'll see the lights...

It would take me longer to explain to an electrician what I want done and exactly how, and then check his work, than it would to just do it myself. :lol_hitti

Do you really think any electrician with any common sense is going to do the "final hookup" and pull the permits on a project you wired? Only an idiot would take on that liability.

I'd probably start by looking on Craigslist...
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Do you really think any electrician with any common sense is going to do the "final hookup" and pull the permits on a project you wired? Only an idiot would take on that liability.

I'd probably start by looking on Craigslist...



Agreed, that is asking for trouble & there is no money in it for the trouble, since they would "own" the job....
 
OP
S

StaggeringGoat

Well-known member
Joined
Jul 1, 2011
Messages
758
Location
Oregon
Do you really think any electrician with any common sense is going to do the "final hookup" and pull the permits on a project you wired? Only an idiot would take on that liability.

That's why the electrician is (getting paid) to inspect and test it. :rolleyes:
 

v8garage

Well-known member
Joined
Jun 27, 2007
Messages
901
Location
Texas
Also said:
ALL[/B] commercial/industial/shop/apartment/etc work is supposed to be done by licensed electricians, not the owner/occupant. Again, YMMV (but I doubt it).

Just because it is that way in NJ doesn't mean it is that way "in almost every locale in the US". I will agree that in most cities in the US it is that way but not in the rural unincorporated areas.
 

dittle fart around

Well-known member
Joined
Jan 9, 2011
Messages
2,455
Location
Vancouver, Washington, USA
Install a 4x4 full size box extension , just like adding another box but this one only has the sides, on the bottom of the existing junction box. Install a twenty amp twist lock outlet in the box extension. Then add a twist lock extension cord out the closest end of the fixture. Twist lock so the plug doesn't fall out. Now your up to code and you can change out the fixtures in the future or move them where you need them.
 

Grumpy365

Well-known member
Joined
Jan 21, 2010
Messages
623
Location
Brazoria County Texas
As a spinoff, I never figured how a inspector ( or NEC) thinks romex is safer stapled to a wall stud than hanging loose in the middle of a wall.

When someone goes to hang drywall or even a picture, they are aiming for the stud and routinely miss by a smidge.

I think you are far more likely to miss the stud and hit & pierce a wire secured to a stud, than if the wire was loose in the wall cavity. PLUS if you try to drive a nail into loose wire with some swing to it, is much more difficult than driving a nail into wire that is secured to a stud.

And for the record I always secure my wires.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
As a spinoff, I never figured how a inspector ( or NEC) thinks romex is safer stapled to a wall stud than hanging loose in the middle of a wall. ...

It is because when stapled you know where it is, if not stapled and floating then it could be anywhere... In that case, anything (nail, screw, etc.) that penetrated the wall might hit a wire.
 

Grazz256

Active member
Joined
Jul 23, 2011
Messages
42
Install a 4x4 full size box extension , just like adding another box but this one only has the sides, on the bottom of the existing junction box. Install a twenty amp twist lock outlet in the box extension. Then add a twist lock extension cord out the closest end of the fixture. Twist lock so the plug doesn't fall out. Now your up to code and you can change out the fixtures in the future or move them where you need them.

We do this with high bay lights, it works great and its easy to swap out a fixture if it breaks.
 

Grumpy365

Well-known member
Joined
Jan 21, 2010
Messages
623
Location
Brazoria County Texas
It is because when stapled you know where it is, if not stapled and floating then it could be anywhere... In that case, anything (nail, screw, etc.) that penetrated the wall might hit a wire.

Ya, I know right where the wire is, 1" from where I need to place a nail, fastned so it won't give when I hit it. :thumbup:
 

slip knot

Well-known member
Joined
Mar 22, 2010
Messages
2,861
Location
Texas gulf coast
This is one area where having a good working relationship with the trades comes in handy. I have an electrician that will pull permits for me and will inspect my work for a marginal fee. I've also had him and his crews completely rewire houses for me in the past and have always paid what was asked. If its over my head He gets the call and if not I take care of it and he signs off. Its a mutual trust thing. He trusts me to know my limitations and I know that he's not going to take advantage of me. My plumbers the same. It really does pay to find a good tradesman and get on his good side. Now if I could just find a good painter that didn't need bail money prior to the work i'd be golden.
 

38Chevy454

Well-known member
Joined
Dec 26, 2006
Messages
4,038
Location
Cincinnati, OH
Is there some part of the code that states if above a certain height (my memory seems to think I have heard 8 ft as the limit?), then exposed romex is acceptable? Or is that old and been superceded? Since the example pic shows wiring on the ceiling, I am sure it is above 8 ft.

I do agree being all in coinduit would look cleaner, but looks vs code is the question here.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
NEC does not expressly forbid Romex or cable or cord in conduit, and in fact, gives information on how to calculate the fill of conduit using cable (Romex is a trademarked name for a brand of cable) or cord, so if the code condones it by specifying conduit fill calculations for it, then it must be OK.