Hi all. I am in the middle of a remodel and we moved the dryer into our garage. I want to hook the dryer back up but the old line is in the attic and won't reach the garage. I have an old 220v line that I used to do some welding with. Can I splice that onto the old dryer line to extend it? I've never spliced a 220 so I don't really know what I'm doing here and I don't want to burn the house down.

Thanks in advance!!
 
To avoid these ads, REGISTER NOW!

gtae07

Well-known member
Joined
Mar 6, 2015
Messages
2,988
Location
Fayetteville, GA
Hi all. I am in the middle of a remodel and we moved the dryer into our garage. I want to hook the dryer back up but the old line is in the attic and won't reach the garage. I have an old 220v line that I used to do some welding with. Can I splice that onto the old dryer line to extend it? I've never spliced a 220 so I don't really know what I'm doing here and I don't want to burn the house down.

Thanks in advance!!

Make sure your extension and the line you used to weld with are the appropriate size of wire for the current. Sometimes using smaller wires is permissible for welders (based on duty cycle etc) but it wouldn't be for a dryer.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
The new receptacle will have to be 4-wire, 3-wire is only allowed in existing installations and if the wiring that the OP wishes to extend does not support a code required 4-wire device it will need to be replaced all the way back to the panel. Dryers are 120/240 volts & it used to be allowed to ground the frame of the dryer to the neutral.
 
OP
M

MarkStanford

Member
Joined
Mar 24, 2017
Messages
16
Nice. Thanks guys. How would you splice it? Would you splice and cap like a typical 110 in a junction or should I splice and electrical tape it? Or is electrical tape a bad idea?

Thanks again. What a great forum. Can't believe I am just discovering this....
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Nice. Thanks guys. How would you splice it? Would you splice and cap like a typical 110 in a junction or should I splice and electrical tape it? Or is electrical tape a bad idea?

Thanks again. What a great forum. Can't believe I am just discovering this....

110 & 220 are pre WWII voltages in North America, current standard is 120V & 240V.

A Ideal® Wingnut® or a 3M® wire connector are good choices, no tape required.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Junction box and wire nuts, do it all the time because when they build houses around here the electrical contractors seem to think Romex doubles as guitar strings and should be pulled tight to at least low E.
 
OP
M

MarkStanford

Member
Joined
Mar 24, 2017
Messages
16
Haha. That's what I was originally thinking - "let's pull these as tight as humanly possible and double bag them with electrical tape". Sounds like overkill.

Thanks guys. Huge help.
 