Any product recommendations to extend neutral service entry wire that comes from the meter into the service panel?

Need to extend the 4/0 aluminum neutral by 6”’and looking to see if there are any good options other than having POCo pull the meter and then running a new cable.

reading through other posts looks like NEC allows it.

something like this may be:

 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Why are you needing to splice it, are you doing a panel change. Is the splice going to be inside the panel. Is the service entrance conductors/cable going to be the right size for the new panel. Is it copper or aluminum. It seems like it is allowed per the NEC
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
Why are you needing to splice it, are you doing a panel change. Is the splice going to be inside the panel. Is the service entrance conductors/cable going to be the right size for the new panel. Is it copper or aluminum. It seems like it is allowed per the NEC
Yes, doing a panel change and need splice because the new panel is bigger and has different layout.
plenty of room in the new panel, so, splice will be inside the panel.
Yes, going from 200a to 200a, no change to service size. The current wire is 4/0 AL. The hots are too long, so, was going to cut them and use one of them as a splice.
Currently service wires are 4/0 AL.
 

klassenl

Well-known member
Joined
Feb 20, 2016
Messages
716
Location
Southern Alberta
In my part of the world you would have to get special permission to do that.

Are you trying to do this without a permit. If you have to get the utility out to pull the meter will you then have to get a permit?
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
In my part of the world you would have to get special permission to do that.

Are you trying to do this without a permit. If you have to get the utility out to pull the meter will you then have to get a permit?
They are not pulling the meter but will shut off the power from the pole. Thats why i mentioned that looking for alternative to running new cable from meter to the panel.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,251
Location
Modesto, CA
Any product recommendations to extend neutral service entry wire that comes from the meter into the service panel?

Need to extend the 4/0 aluminum neutral by 6”’and looking to see if there are any good options other than having POCo pull the meter and then running a new cable.

reading through other posts looks like NEC allows it.

something like this may be:

I wouldnt use the splice kit you linked to. thats for underground use as it has gel in it. use kearney bolts or split bolts...
Here they don’t allow splices in the panel, because it is not a junction box.
Is that a local WRITTEN amendment?
In my part of the world you would have to get special permission to do that.

Are you trying to do this without a permit. If you have to get the utility out to pull the meter will you then have to get a permit?
youre in canada. many parts of the US do not require permits for electrical work.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,996
Location
Thousand Islands NYS
"Here they don’t allow splices in the panel, because it is not a junction box."

In my experience, it has to do with the listing. It seems to often be allowed but I would check it out with inspector before mounting.
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
I wouldnt use the splice kit you linked to. thats for underground use as it has gel in it. use kearney bolts or split bolts...
Great info, thx.
Adding to this, what type of connector would you recommend to extend branch circuits? I will need to extend couple of hot wires on 15a and 20a circuits.
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
Split bolt wrapped with splicing tape on the service wire.
Tan wire nuts on smaller wires
Thank you.
you mean something like below for split bolt?

 
To avoid these ads, REGISTER NOW!
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
Fine to splice wire as long as there is space for the splice in the box (not allowed in conduit). Use https://www.homedepot.com/p/Dual-Ra...lid-Barrier-Wire-Stop-ASR2506-B1-10/100190266 if service neutral that doesn't need insulated.

Thank you.
What determines if neutral should be insulated? I have seen both around here: insulated 4/0 wires for hots and neutral and neutral being braided strands around hot wires.

Can I use splicing tape to cover up the bolt that you linked to?
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,613
Location
SE MI
Great info, thx.
Adding to this, what type of connector would you recommend to extend branch circuits? I will need to extend couple of hot wires on 15a and 20a circuits.
Assuming it is inside of a box, wire nuts/Marettes are fine. If the splice needs to be done where there is no box, a box must be added.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
I wrap it with inside out super33 around the split bolt 1st,then this stuff.
Then I go back over it with 33 the regular way.
 

Attachments

  • 20210819_130800.jpg
    20210819_130800.jpg
    166.4 KB · Views: 19

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Thank you.
you mean something like below for split bolt?

Yes,that's a split bolt.
 

FMB4

Well-known member
Joined
Jan 19, 2017
Messages
2,926
Just do it right and have POCo pull the meter and run a new cable. Btw, aluminum wiring is not a good idea imo.
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
Just do it right and have POCo pull the meter and run a new cable. Btw, aluminum wiring is not a good idea imo.
What are the concerns with aluminum cable? I read that folks like them because they are flexible.
 
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
Yes,that's a split bolt.
Looks like big box stores around here are out of stock on them. What are the thoughts on using the connector that user “stuff” shared above along with splicing tape?

 
Last edited:

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Looks like big box stores around here are out of stock on them. What are the thoughts on using the connector that user “stuff” shared above along with splicing tape?

Those would work also. As far as splicing in the panel, we are allowed to do it here. We are allowed to extend conductors to reach to breakers and lugs. Always check with local codes. I personally never splice the service feeders, but thats just me. But then, being licensed here, Im allowed to pull meters to replace the cable. So it sounds like you are doing this hot
 
Last edited:
OP
M

Mike1903

Well-known member
Joined
Jan 16, 2021
Messages
139
Location
Suburbs
Those would work also. As far as splicing in the panel, we are allowed to do it here. We are allowed to extend conductors to reach to breakers and lugs. Always check with local codes. I personally never splice the service feeders, but thats just me. But then, being licensed here, Im allowed to pull meters to replace the cable. So it sounds like you are doing this hot
Thanks for sharing the thoughts. I am having power disconnected for some other work; it won’t be hot.
 