To avoid these ads, REGISTER NOW!

extension cord w/ 240v and 120v?

Buickspec6231

Well-known member
Joined
Jun 14, 2018
Messages
127
Location
CNY
Has anyone made their own outlets/box to plug in their 240v extension cord into that also has a 120v outlet on it, like on a generator? If I am running a welder, I am also going to be using the grinder for surface prep or whatever. Trying to limit the amount of extension cords I am dragging around the shop floor. I was thinking I could just pull 120v off of one of the conductors for the 240V outlet and wire it to a 120v 15amp outlet in the same box. I am no electrical engineer and have limited experience with residential wiring. I'm sure it is more complicated than the doodle I have attached, but to me it makes sense. Also, I'm not opposed to a commercially available product, just can't seem to find one. Which could also be taken as a sign. Be easy on me if this is a terrible idea. I'm just brainstorming. The receptacle is wired with 6/3 from the box on a 40a breaker and the extension cord is 8/3. Combined total length from breaker to end of extension cord does not exceed 55ft. IMG_20180731_201604349.jpg
 
Last edited:
To avoid these ads, REGISTER NOW!

Hdonly0

Well-known member
Joined
May 16, 2017
Messages
114
Location
Northwest Florida
You should be using a four wire extension cable with two hots, neutral, and ground. I would also install one of these circuit breakers in your box at the cable end on the 120 volt receptacle. Otherwise you are running a 40 amp circuit to a 15 amp 120 volt receptacle.

attachment.php
 

Attachments

  • breaker_.jpg
    breaker_.jpg
    85.5 KB · Views: 352

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,670
Location
SE MI
A couple of years ago, there was a thread about a DIY power distribution box. This is what you want.

EDIT : I could not find it but this is the best way to do want you want.


  • Your feed must have 4 wires and should have a NEMA 14-20 or 14-30 plug (locking or non-locking). @ hots, neutral and ground
  • Buy a small (2/4 or 4/8 space/circuit) breaker box, preferably one that is surface mounted. Look for one that has a lot of extra space on the inside.
  • Make cut outs on the side for NEMA 5-15 duplex receptacles and NEMA 14-20/30 outlets.


Install receptacles. Wiring will be very tight, but it is doable!
 
Last edited:
OP
B

Buickspec6231

Well-known member
Joined
Jun 14, 2018
Messages
127
Location
CNY
Are you recommending the 4 conductor wire plus bare ground so that I am not sharing the ground with the neutral on the 120v outlet? I'm much more comfortable with 12v automotive wiring where this whole neutral problem doesn't exist. Thank you for the quick replies and the component recommendations. The in-line breaker makes sense. I started looking at available units (after theoldwizard taught me what they are called), and I don't really want/need one the size of the commercially available units. I'm going to start pricing out what I really need and see how that compares to a store bought model. Learning as we go along.
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
Are you recommending the 4 conductor wire plus bare ground so that I am not sharing the ground with the neutral on the 120v outlet?

It's 4 conductors, including ground, all insulated. Typical color coding is black and red for your 240v legs, white for neutral, and green for ground.
 
OP
B

Buickspec6231

Well-known member
Joined
Jun 14, 2018
Messages
127
Location
CNY
That makes more sense to me now. I'm going to be adding this to my list of projects. So far it's looking like a way better plan.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Don't mess with this, run a smaller cord for a grinder. You need new outlet, new cord, extra overcurrent protection, gfci.
 
Last edited:

driftpin

Well-known member
Joined
Dec 22, 2016
Messages
11,439
Location
Miami-Dade/Broward Co. Florida
Don't mess with this, run a smaller cord for a grinder. You need new outlet, new cord, extra overcurrent protection, gfci.

This sounds better to me, anytime electricity is involved, better to be safe than sorry. You could probably jury-rig something but rather than 'share' a hot lead, having the right configuration sounds like a better choice to me.

Couldn't you just zip-tie the two cords together, if you want-to keep things neat?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Have you ever seen a spider box?

Usually they are fed 208Y/120 50a or 100a and then theres individual breakers for the 120v outlets.

You would need separate overcurrent protection for the 120v outlet.
 
To avoid these ads, REGISTER NOW!

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I'd run the main to a 4" box with the welder outlet, then split off to a quad with a GFCI and the bitty breaker pictured above. Done.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The only way that is legal is if it is plugged in to a 20A circuit. Maybe not even then since it now is not gfci.
If I am on projects often the grinder cord really isn't long enough anyway. It would need to be plugged in with the cart and machine close to the work and not allow much movement.
Outlets on fixed benches is good, other than that a cheap orange cord. Lay it along the same pathway as the welder cord if that's an issue, often it doesn't have to come from the same direction. I have economy cord reel in a couple places, can even put those overhead.
The fact that I can build any of this I want,,,,,, am a gadget builder,,, and don't says a lot. Especially as I refine,,, get a little older, find out simpler is good and maybe better. I actually got rid of a lot of that type of stuff during remodels. Don't need to use every fitting they ever invented.
 

Attachments

  • bench sp door.jpg
    bench sp door.jpg
    149.8 KB · Views: 34
  • cutting can.JPG
    cutting can.JPG
    39.7 KB · Views: 32
  • ground coord reel.jpg
    ground coord reel.jpg
    76.3 KB · Views: 32
Last edited:

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,670
Location
SE MI
Are you recommending the 4 conductor wire plus bare ground so that I am not sharing the ground with the neutral on the 120v outlet?
It's 4 conductors, including ground, all insulated. Typical color coding is black and red for your 240v legs, white for neutral, and green for ground.
In "portable cordage" (the industry term for extension cord wire) they count all of the conductors including the ground. Matt is correct in that there are not "bare" conductors.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,670
Location
SE MI
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Ya, I have seen a couple of these gems at fleas, not a bit of writing on it. Another 30 to 15. could plug a power strip in to it I spose.
Wiz,,, that one you posted says UL, wonder how that is so? Maybe someone with minds greater than our own can explain it? seems like there would need to be a breaker. They say something about generators, wonder if there is something around that?
I don't recall any overcurrent on welders, cant recall if they had something internal self resetting etc. My helper is gone a couple days, I will have to ask him. It seems I wonder that before but didn't ask anyone. I am sure someone here knows.
 

Attachments

  • adapt 30.jpg
    adapt 30.jpg
    132.2 KB · Views: 28
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Ya, I have seen a couple of these gems at fleas, not a bit of writing on it. Another 30 to 15. could plug a power strip in to it I spose.
Wiz,,, that one you posted says UL, wonder how that is so? Maybe someone with minds greater than our own can explain it? seems like there would need to be a breaker. They say something about generators, wonder if there is something around that?
I don't recall any overcurrent on welders, cant recall if they had something internal self resetting etc. My helper is gone a couple days, I will have to ask him. It seems I wonder that before but didn't ask anyone. I am sure someone here knows.

Wheres the U/L wrap around sticker?

I dont see one. Maybe i missed it...
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,981
What's wrong with attaching a 120V cord to your 240 cord with tape every couple of feet? It rolls up and goes out as a single element, not much more work.
 
To avoid these ads, REGISTER NOW!