Failed GFCI, outlet type. Potential Causes?

svtride

Well-known member
Joined
Sep 6, 2009
Messages
201
Edit: 20 15 amp rated Leviton outlet, ~17 years old though barely-to-never used. Outlet installed by licensed electrical contractor when shop built. Located inside, dry location. Went to use and noted no green light. Pushed the reset button and “flash / pop” shot out of blade receptacles. Very startling.
1. What would cause this?
2. Do I have a latent electrical issue lurking in my building?
3. Are these type of receptacles life limited?
4. What about the other still functioning (~6) in other circuits throughout my shop…replace them preemptively?

Disassembled
GRAB85.jpg
 
Last edited:
To avoid these ads, REGISTER NOW!

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,284
Location
Hunterdon County NJ
20amp rated Leviton outlet, ~17 years old though barely-to-never used. Outlet installed by licensed electrical contractor when shop built. Located inside, dry location. Went to use and noted no green light. Pushed the reset button and “flash / pop” shot out of blade receptacles. Very startling.
1. What would cause this? Short to ground on 'down stream' wires or wire touching ground in box
2. Do I have a latent electrical issue lurking in my building? Maybe but can’t tell without testing
3. Are these type of receptacles life limited? NO……. But it depends on the environment
4. What about the other still functioning (~6) in other circuits throughout my shop…replace them preemptively? NO…… But they should be checked out by a qualified electrician.
I think the GFI "tripped" because of a ground fault then you pushed the reset button and BAM! the receptacle faulted. Check ALL the wiring before replacing the GFI receptacle.

TIP! CALL A PRO if you don’t know what you are doing!…….. This is my best advice.
 
To avoid these ads, REGISTER NOW!
OP
S

svtride

Well-known member
Joined
Sep 6, 2009
Messages
201
How come the neutral Tee slots are solid (not cut out) if its a 20A?

As to the **** , lightning maybe.
Upon further examination, the outlet is in fact 15amp. Correction made in OP. The branch's circuit breaker is 20 amp, wired with 12AWG. EDIT some more: I did some more garage barrel diving as I had thrown out the whole GFCI and found this label that I thought had planted the 20 amp rating in my head. I pulled another of the GFCIs from another location in shop and it had the same label but also no tee slot cutout though the tee slot plastic component of GFCI had “15a” molded into it.
I thought, disappointedly, I had 15amp outlets in 20amp protected circuits..but these stickers indicate correct rating for outlet, though with no Tee slots. What’s up with that? GRAB89.jpg
Because it's a 15A duplex GFCI.

@svtride any chance this is in a metal shop?

Looks like a dead short to me. Did breaker trip?
Not a dedicated metal shop but I do some metal work at times, mostly personnel vehicle mechanical repairs and service, hobbyist, nothing commercial. Outlet is in opposite area of shop where only vehicles are stored, no work performed. Breaker had not tripped but did when I attempted to reset GFCI, BAM.
Wild guess here, but did you have any lightning storms in the area? I have seen lightning do some "wacky things" on an electrical system.
Two large storms involving lightening in recent week with a neighbor losing power (I did not) when transformer blew on utility pole that serviced his house and another.
Agree, we had a lightening strike a maple tree several years ago and over next days got whiffs of nature gas smell. Called utility, they investigated and sure enough lightening zapped a hole in gas service pipe that ran by tree to house.
 
Last edited:

JohnC1957

Well-known member
Joined
Mar 19, 2022
Messages
84
Mine seem to age out. Replacing them has been a first step and I have never had to go further. That's the extent of my knowledge ! I totally required in 2010 and half have been replaced
 