I am in planning phase for electrical. Looking to do a 100 amp sub panel in the garage. Going to surface mount to interior plywood wall and run conduit.
Question is are there panels with the lugs at the bottom? I have a 1 foot stem wall so i'll be coming up and over that but in at the two foot aprox height. Do i just mount it upside down?
 
To avoid these ads, REGISTER NOW!

ForceFed70

Well-known member
Joined
Apr 27, 2010
Messages
3,441
Location
BC, Canada
Most panels are designed such that they can be mounted upside down. Check the manufacturers specification.
 

teamextreme

Well-known member
Joined
Aug 10, 2013
Messages
867
Location
Lakewood, CO
If not, there's nothing wrong with running the wires up through the panel to the top and looping them back down into top-mounted lugs. Done all the time, just requires a couple more feet of wire.
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,949
Location
New England
If not, there's nothing wrong with running the wires up through the panel to the top and looping them back down into top-mounted lugs. Done all the time, just requires a couple more feet of wire.



Thanks Easy enough


Sent from my iPhone using Tapatalk
 

malibu101

Well-known member
Joined
Jul 1, 2005
Messages
3,910
Location
Walnutport PA
My understanding has been that----
If the main breaker handle moves horizontally- it doesn't matter
BUT
If the main breaker handles moves vertically- up must be on and, obviously, down must be off.
 

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,443
Location
Western North Carolina
My understanding has been that----
If the main breaker handle moves horizontally- it doesn't matter
BUT
If the main breaker handles moves vertically- up must be on and, obviously, down must be off.

Just to clarify, the other breakers can be installed being on while handle down?
 
To avoid these ads, REGISTER NOW!

stonesg

Well-known member
Joined
Jun 13, 2016
Messages
249
Location
SE Georgia
My main panel is a Square D and it's fed to lugs on the bottom with a horizontal main.

Probably happens a lot in sub divisions like mine where all the power lines are buried.
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,949
Location
New England
One note on that sub....if you get more than 6 breakers, you have to have a main breaker



It is detached and I will definitely have more then six. So in house panel I have a 100amp breaker and the sub has a 100 main breaker?


Sent from my iPhone using Tapatalk
 
OP
K

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,949
Location
New England
Bottom fed panels are not “upside down “.

I wasn’t sure if there are panels specifically made with the lugs at the bottom and all the printed stuff that way as well or if it’s a normal panel turned like the Canadians do.


Sent from my iPhone using Tapatalk
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,978
It is detached and I will definitely have more then six. So in house panel I have a 100amp breaker and the sub has a 100 main breaker?

Yes. The breaker in the sub is just serving as a disconnect, so it can be rated higher than the breaker feeding it. In other words, you can feed a 100A main breaker subpanel with a 90 or 60A breaker. People do that because the wire cost is lower, they don't really need 100A in the garage, and 100A main panels are common and cheaper (and have more spaces) than 60A ones.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,354
Location
Alexandria, VA
I installed a Square D 100 amp sub-panel and fed it from conduit connected to the bottom. However, I just ran the incoming wiring (2-2-2-4 AL) longer and routed it up inside the panel so I could leave the main breaker at the top. There was plenty of space to make the turns in the wire. I just liked the look of the panel better with the main breaker at the top.

Bruce
 