Feeder cable routing

dmm42

New member
Joined
Sep 22, 2023
Messages
1
I just upgraded my service from 150A to 200A. My garage currently has only one circuit that is shared with part of the basement. Im planning on installing a minimum of a 60A subpanel in the garage; I plan on having a few circuits for lights, receptacles for tools, and possibly a heater/AC for projects when the weather is at its extremes. I’m possibly leaning towards 100A in order to future proof a bit.

What would be the most efficient method to route feeder cable from the panel, across an unfinished basement, and into the garage. There is concrete blocking around the bottom perimeter of the garage. I’d like to
have the panel above the black tool chest in the attached photos.

 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,112
Location
Central Iowa
With #2 SER cable, I would use 1-1/4 or 1-1/2 PVC on the bottom of the joists to get to the pocket you need. Then run between the joist to get to where you need to be. Go through the wall with a piece of PVC into an LB and run it into the panel. And use a 90 amp breaker in the main panel, that way, you will be code compliant. We don't like 100 amp breakers connected to 100 amp feeders. :thumbup:
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,786
With #2 SER cable, I would use 1-1/4 or 1-1/2 PVC on the bottom of the joists to get to the pocket you need. Then run between the joist to get to where you need to be. Go through the wall with a piece of PVC into an LB and run it into the panel. And use a 90 amp breaker in the main panel, that way, you will be code compliant. We don't like 100 amp breakers connected to 100 amp feeders. :thumbup:
You mean we don't like 100 amp breakers connected to 90 amp feeders? :)
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,630
Location
BC
Typical economical route for doing that around here is armoured cable with aluminum conductors. #2 on a 90A breaker is appropriate, unless the distance is especially long.
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,994
Location
Thousand Islands NYS
If run across basement ceiling was perpendicular to joists, I would probably do what Sparky said. My inspector would not approve SER fastened to bottom of joists and I think he's correct by code. And I'm not going to drill holes and pull no. 2 aluminum SER through them. If looks and headroom don't matter, you could protect it with a 1x3 or similar nailed across joists and fasten to that.
 