how high above ground does a feeder entry to a detached garage need to be? assuming underground feeder and PVC LB. from the NEC it seems 18" but man that document is hard to read.
You might be confusing burial depth. There is no requirement.
I would come out of the ground and go 5' up the wall and LB straight into the upper backside of the panel.
What is the insulation type on the cable/conductors are you running?




hmm well I know the burial depth is 18". I'm using 2" sch 40 PVC. I could swear I read something about a minimum entry height, or it could've been a minimum height that needed protection from physical damage??
in any case I'd rather not go too high because it would look odd.
for wire I was planning a 2-2-2-4 mobile home feeder or separate XHHW wires, although I'm not quite sure what AWG I need for the separate conductors. 1-1-1-6 if I go with Cu?? I wanted 100A service to the garage.
hmm well I know the burial depth is 18". I'm using 2" sch 40 PVC. I could swear I read something about a minimum entry height, or it could've been a minimum height that needed protection from physical damage??
in any case I'd rather not go too high because it would look odd.
for wire I was planning a 2-2-2-4 mobile home feeder or separate XHHW wires, although I'm not quite sure what AWG I need for the separate conductors. 1-1-1-6 if I go with Cu?? I wanted 100A service to the garage.
so i've never pulled large cables through underground conduit. is #1 al really that hard to pull? I'm a bit wary of getting half way through it and getting stuck. that's why I bought 2" conduit. I didn't buy wire yet so I have options.
what insulation would you use for this? i know there's USE2, URD, thhn, etc. I've got the conduit so figured direct bury wire would be a waste and hard to pull.
so i've never pulled large cables through underground conduit. is #1 al really that hard to pull? I'm a bit wary of getting half way through it and getting stuck. that's why I bought 2" conduit. I didn't buy wire yet so I have options.
what insulation would you use for this? i know there's USE2, URD, thhn, etc. I've got the conduit so figured direct bury wire would be a waste and hard to pull.
I also suggest Al XHHW-2. Since you'll be using individual conductors you don't need a #3 Al EGC as suggested by mm08822, #6 Al is good up to 100A. Assembled jacketed cable such as SER will come in the size 1-1-1-3. Be mindful that SER is not allowed underground even if in conduit. Also URD is not allowed inside of the structure. The pull of #1Al through 2" conduit should be a breeze.
Whoops, wrote too many 1's too quickly. #3 was meant for the neutral not the grd.
Yes, agreed 1-1-3-6 AL XHHW works.![]()
What is the criteria for a reduced neutral? Would that work in a shop that has mostly 120v equipment?
I'm not an electrician, but my son and I pulled Cu 2-2-2-4 THHN/THWN through 2" conduit.
The pull was 250ft.
It was not really hard until we hit the 90 turns. I had several. I used a heavy nylon rope and a lot of wire lube. At one point we got totally stuck. I attached the rope to my truck bumper and gave a light tug. It pulled right through.
You should be fine.
gotta be careful with round rope. it can burn through 90's due to the friction, like a hot knife cutting through butter.
flat mule tape is made for this reason...
I've been pulling through pvc for 20 years with round rope and my Maxis puller. Never had a problem. Not arguing the mule tape point. But the puller doesn't grip the mule tape as it does the pulling rope. And I have a very old Greenlee puller that was designed for pulling rope.
I'm not positive, but I believe you can re-identify the neutral by wrapping white tape around it (it's allowed on wires 4 gauge and bigger), but not the ground wire.
exranger I get that for XHHW when you look at table 310.13. but for XHHW-2 it says 90C for wet applications which undergound conduit is... so where is the requirement to use 75C? it may well be in there somewhere I just don't see it.
How could you know whether the 90s got burned through when the conduit is underground?
Same way you know that they didn't when you used mule tape.
The standard practice here for underground residential services is to use type USE "triplex" or "urd" (both local slangs). Which is direct burial rated, and also sunlight rated. So if, in fact, a 90 "got burned", it really doesn't matter. (unless, of course, the cable/ conductors were also damaged. I don't go so far as to megger each pull.
I really don't understand your doom and gloom outlook on pulling rope. But if I shared the fear, I'd use rigid 90's, as allowed by the NEC, to reduce this friction.
Maybe because ive seen them burned through
so rather than pull the 125ft of cable through the buried conduit I was thinking of setting the cable in the trench and then sliding the conduit sections over it one by one and gluing them as I go.
is there any reason this wouldn't work?? seems like it would be much easier than trying to pull 125ft of 1-1-1-6 through a 2" pipe.
I do have one wide 90deg turn I need to make. maybe a 5ft radius or as wide as I need it to be. figured I could just bend the conduit and shove it in the trench.
so rather than pull the 125ft of cable through the buried conduit I was thinking of setting the cable in the trench and then sliding the conduit sections over it one by one and gluing them as I go.
is there any reason this wouldn't work?? seems like it would be much easier than trying to pull 125ft of 1-1-1-6 through a 2" pipe.
I do have one wide 90deg turn I need to make. maybe a 5ft radius or as wide as I need it to be. figured I could just bend the conduit and shove it in the trench.