I am trying to figure out what size neutral i need to run for my sub-panel. I went to school for this and went to work for a utility and don't use this any more. Its in a detached residential garage. I am running a 100 amp sub with #1 AL, and a #6 CU grnd. My confusion comes into sizing the neutral. I hve been looking at annex D, and 220.*** and have come up with a #6 CU/4 AL for a neutral. I was hoping someone that deal with this stuff on a regular basis could double check my work. I used the residential dwelling standard for 3va per sq ft. I have 2160sq ft X 3VA=6480
50 amp welder 12kva
30 amp compressor 5760
1 required 20 amp circuit 1920
That gives me a total of 26160 va
1st 3k @100% = 3000
rest at 35% 23160 X .35 = 8106
8106+3000=11106
11106/240=46.275
Next biggest size is 50 amp #6/#4
Does this look right? Am i missing anything? Thanks for the help