Picking wire out for a buddy's barn and wanted to ask about neutral and ground sizing
setup is:
-2" conduit, approx 125' end to end.
-Breaker in house will be somewhere between 60a and 90a, depending on what is available locally.
-Wire will be AL XHHW-2
1st Question - I can't relabel a black conductor as ground, correct?
2nd Question - If the answer above is that I can't relabel it, the cheapest option appears to be a 500' spool of #2 for both hots and the neutral (identifying the neutral with white tape) and a ~150' length of green #6 for ground
The barn will also get two ground rods and the neutral bar will be unbonded from the subpanel.
any issues/recommendations? thanks!