Few questions about mini split removal and new install

Tracs

Well-known member
Joined
Feb 1, 2015
Messages
569
Location
Manitoba, Canada
I am getting ready to remove my PerfectAire mini split and install a new Napoleon Oasis NH25-18F Hyper heat unit in my detached garage.

The current unit is mounted on a cement pad with a lineset length of 10'.

The new unit will be mounted on the wall with a bracket to get it off the ground. The Napoleon unit will make some heat down to -22F and we get lots of snow so I want to have it up on the wall so it doesn't freeze up, like the PerfectAire unit did.

I don't know where the best place or height to mount it would be. I throw some outdoor odds and ends in the back corner behind the garage but only go back there a couple times a year. From the garage to the fence it is 3' of room.

The lineset is the same size for each unit. Can I re-flare/re-use the current lineset?

Can I pressure test the lines with 100% Argon gas or C25 Welding gas? I have both and the regulators for the required pressure. But I might be almost out of Argon.

From the supplied pictures, where would the best location for the new wall mounted unit be?

Ideally I would like to keep the new unit relatively in the same location, just up on the wall 2' or so off the ground so it doesn't ice up.


20140612_095849.jpgPXL_20221010_195027014.jpgPXL_20221010_195052274.jpg
 
To avoid these ads, REGISTER NOW!

jlv03

Well-known member
Joined
Jan 19, 2020
Messages
349
Location
SE IA
Since you already have the concrete pad, any thoughts on just using an elevated stand?
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,685
Location
Maine
You need it higher if you get snow?? They make metal brackets that will get 2ft or so off ground
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,417
Location
N CA
You can get some harmonics on a wall mount. I have a 24 dual that I can hear in one room. Not objectionable as that room is lightly used, but you can hear the unit. I’m with Walrus on your height get it up there.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,995
Location
Peace Valley,mo
Nitrogen is recommended for testing for system leaks and breaking of a vacuum for a triple evacuation. Most systems check at 500 to 600 lbs.
 
OP
T

Tracs

Well-known member
Joined
Feb 1, 2015
Messages
569
Location
Manitoba, Canada
I was checking out a unit at work today. It is mounted 4' off the ground on wall brackets. I liked that height, won't ever get snow buildup on it up there.

The problem becomes at that height and location the lineset would only be 6' long.

I also know nitrogen is recommended for testing for leaks, but I have the Argon.
 

Kobuck

Member
Joined
Jul 21, 2020
Messages
23
Location
Ohio
I was checking out a unit at work today. It is mounted 4' off the ground on wall brackets. I liked that height, won't ever get snow buildup on it up there.

The problem becomes at that height and location the lineset would only be 6' long.

I also know nitrogen is recommended for testing for leaks, but I have the Argon.
Argon is inert. It will work
 
To avoid these ads, REGISTER NOW!
OP
T

Tracs

Well-known member
Joined
Feb 1, 2015
Messages
569
Location
Manitoba, Canada
Are any of these amazon mounting brackets any good, and any better than what the local HVAC supply house will have for 2-3x the cost?

I probably couldn't buy some angle iron and build one that cheap.


 

Phuckin' Jim

Well-known member
Joined
May 16, 2009
Messages
235
Location
North of the Peg
Those stainless ones are pretty sweet!
Bed frames can be had for free, and you could build brackets out of that, if you are looking to save cash.
If free bed frames can't be found, check scrap yards like Orloff for inexpensive steel sold by the lb. 😁
 

justinjoyal

Well-known member
Joined
Apr 30, 2015
Messages
888
Location
Quebec
Since you already have a pad I would definitely not recommend mounting the new unit on the walls as it could get noisy inside.

Re-use the pad with a stand.

If you know the previous system was properly installed and was functioning properly (ie no compressor burnout, no leaks, etc) I would not be worried about using the existing lineset.
 
OP
T

Tracs

Well-known member
Joined
Feb 1, 2015
Messages
569
Location
Manitoba, Canada
Since you already have a pad I would definitely not recommend mounting the new unit on the walls as it could get noisy inside.

Re-use the pad with a stand.

If you know the previous system was properly installed and was functioning properly (ie no compressor burnout, no leaks, etc) I would not be worried about using the existing lineset.

If I use a stand on the pad where it is, I don't know what to do about the linest length. It would only be about 6'-7' long.
 

mogandave

Well-known member
Joined
Nov 4, 2021
Messages
3,052
Location
Bangkok
Splits are mounted on walls the world over. My last home had five splits, and four of five had the condensers mounted to the second-floor walls.

My current home has seven, with none mounted on the walls, but only because there are ledges & balconies mount them on. They are still all mounted directly to the building. When I renovate, I'm hoping to move them all to the roof.

It is pretty common the world over to mount them on the walls, ledges and balconies.
 
OP
T

Tracs

Well-known member
Joined
Feb 1, 2015
Messages
569
Location
Manitoba, Canada
Splits are mounted on walls the world over. My last home had five splits, and four of five had the condensers mounted to the second-floor walls.

My current home has seven, with none mounted on the walls, but only because there are ledges & balconies mount them on. They are still all mounted directly to the building. When I renovate, I'm hoping to move them all to the roof.

It is pretty common the world over to mount them on the walls, ledges and balconies.

I'm not overly concerned with mounting it on the wall. It is a garage I spend little time in.
 

jjrbus

Well-known member
Joined
Dec 8, 2018
Messages
619
Location
Florida
Run the line in a serpentine fashion behind the condenser to get to the required length.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,730
Location
Fargo, ND
Are any of these amazon mounting brackets any good, and any better than what the local HVAC supply house will have for 2-3x the cost?

I probably couldn't buy some angle iron and build one that cheap.


This looks like the one we sold at work, good wall mount, flexible as you can mount the upper bar to the wall and slide the supports to the left or right, where ever you need them.
Contractor price was under $100 a couple years ago.
 
OP
T

Tracs

Well-known member
Joined
Feb 1, 2015
Messages
569
Location
Manitoba, Canada
I picked up 2 different brackets from my HVAC supply just Incase I decide to mount it on the wall. I still haven't decided. One is the foldable kind and the other is nice coated fixed angle iron type. Glad I didn't think Amazon was going to be cheaper. 2 brackets and a 90 degree linset elbow was only $78.
 
OP
T

Tracs

Well-known member
Joined
Feb 1, 2015
Messages
569
Location
Manitoba, Canada
I think I have settled on a plan as pictured in this crude ms paint picture.

The unit will be mounted 4' off the ground on the wall using the brackets I picked up. The current lineset will come down 6' then over 4' to the new unit. I will use rubber isolation mounts in between the unit and the brackets. mounts.JPG

PXL_20221010_195027014a.jpgPXL_20221021_224406223.jpgPXL_20221022_011001566.jpg
 