I put down a deposit today for my shop build. Build thread to follow when things start moving forward. It is going to be a 32x44. I am currently thinking through the electrical needs. My plan is to run a 100 subpanel off the main house panel. Currently has a 150 amp main, but will be upgraded to a 200amp. All of my appliances are gas minus the heater.
I plan on having a/c, possibly a 36,000BTU mini split. My worst case will be using my plasma cutter while the a/c is running and the air compressor kicks on. Doing a quick calculation, figuring 32 amps for the compressor while running (7.5hp, not 100% on brand yet), 18 amps for the plasma per hypertherms information, and 28 amps for the a/c, I come up with a total of 18,960 watts or 79 amps.
My math seems to indicate that I will be fine but I wanted to make sure I wasn't missing anything. It will only be me out there, lights will be LED, so no real potential for any other large amp draws other than my "worst case".
Thoughts?
I plan on having a/c, possibly a 36,000BTU mini split. My worst case will be using my plasma cutter while the a/c is running and the air compressor kicks on. Doing a quick calculation, figuring 32 amps for the compressor while running (7.5hp, not 100% on brand yet), 18 amps for the plasma per hypertherms information, and 28 amps for the a/c, I come up with a total of 18,960 watts or 79 amps.