I will be building a 50x80x14 machine shed in the next few months. I have a reasonable idea of what I will have done for this but I would like some feedback before actual work starts.
The building will be a 50x80x14 pole barn with a concrete floor with a vapor barrier underneath, and condensation barrier on the inside of the sheathing. Trusses 4' on center and poles 8' on center, and rafters will be open to below. There will be four 16x12 overhead doors and a man door on one sidewall, no windows, and no HVAC or plumbing inside the building, and nothing on the other sidewall or either end wall. Garage doors will be on electric openers.
This will be located on rural farmland. According to the contractors I have bid the project with, utility power will nearly certainly be a 320/400 A single-phase service that comes in overhead to a pole-mounted transformer sitting between the house and the building. The meter base will have multiple disconnects and one of the feeders from the meter base will go to the outbuilding, and the feeders from the meter base to the house and building will be buried.
I will be using the building for equipment storage (mainly hay equipment) and maintenance. The first project I will do in the building other than put the hay equipment in there will be to restore my family's 1965 John Deere 110 but larger projects will follow. I will have a good-sized air compressor and welder in the future which will go in the outbuilding. Anything else I could think to use there for tools would 20 amps or less on 240 volts, such as my pedestal grinder or a bandsaw, or 120 volt hand tools.
My thoughts are:
1. 100 amp service to the outbuilding. I did a guesstimate load calc with a 7.5 hp air compressor, 50 amp welder, and fluorescent lighting to give a worst-case scenario and the draw was right at 100 amps. I'd use a 20-24 space panel to make sure to have enough circuits. Any feedback on this?
2. Lighting to the typical ~90 fc range so I can see well. I did quite a bit of reading of this forum and played with the Visual 3D tool and came up with three options:
- 12k lumen 2' linear LED highbays (such as Lithonia IBE), 7x6 arrangement, 4' in from each end and then every third rafter (12') in between and six per rafter. This would be wired to two 120 volt 20 amp circuits.
- 15k lumen 2' linear LED highbays, 7x5 arrangement identical to above but one fewer fixture per rafter. Would be wired similarly.
- 6-lamp T8 highbays (e.g. Lithonia IBZ), 7x6 arrangement identical to the 12k lm LED setup. These would be using linear LED bulbs.
The questions I have are:
a) Are the 12k lumen or 15k lumen fixtures better for this application with a ~14' mounting height? 14' seems to be in a gray area where there doesn't seem to be a clear recommendation as to which one is better.
b) Are the integrated LED fixtures or replaceable-bulb linear LED fixtures recommended? I am a little leery of getting an integrated LED fixture because if something fails, the entire fixture must be replaced and it would be very likely that whatever new fixture is available at the time would be dissimilar to the ones already in use. I did a bunch of reading on this topic and nobody ever seemed to answer the question.
3. I will have outdoor lights over the overhead doors. I would like to have this on a switch controlled inside of the house so I can see to go outside there in the dark but not have the place lit up every night using a dusk to dawn light/lights. Since the building will nearly certainly be supplied from the pole rather than being a subpanel from the house, would it be worthwhile to do this the conventional way of running a conduit to the house for a separate outdoor lighting circuit or would another means such as a remote-controlled switch be better, and if so, which one?
Thank you for your input.
The building will be a 50x80x14 pole barn with a concrete floor with a vapor barrier underneath, and condensation barrier on the inside of the sheathing. Trusses 4' on center and poles 8' on center, and rafters will be open to below. There will be four 16x12 overhead doors and a man door on one sidewall, no windows, and no HVAC or plumbing inside the building, and nothing on the other sidewall or either end wall. Garage doors will be on electric openers.
This will be located on rural farmland. According to the contractors I have bid the project with, utility power will nearly certainly be a 320/400 A single-phase service that comes in overhead to a pole-mounted transformer sitting between the house and the building. The meter base will have multiple disconnects and one of the feeders from the meter base will go to the outbuilding, and the feeders from the meter base to the house and building will be buried.
I will be using the building for equipment storage (mainly hay equipment) and maintenance. The first project I will do in the building other than put the hay equipment in there will be to restore my family's 1965 John Deere 110 but larger projects will follow. I will have a good-sized air compressor and welder in the future which will go in the outbuilding. Anything else I could think to use there for tools would 20 amps or less on 240 volts, such as my pedestal grinder or a bandsaw, or 120 volt hand tools.
My thoughts are:
1. 100 amp service to the outbuilding. I did a guesstimate load calc with a 7.5 hp air compressor, 50 amp welder, and fluorescent lighting to give a worst-case scenario and the draw was right at 100 amps. I'd use a 20-24 space panel to make sure to have enough circuits. Any feedback on this?
2. Lighting to the typical ~90 fc range so I can see well. I did quite a bit of reading of this forum and played with the Visual 3D tool and came up with three options:
- 12k lumen 2' linear LED highbays (such as Lithonia IBE), 7x6 arrangement, 4' in from each end and then every third rafter (12') in between and six per rafter. This would be wired to two 120 volt 20 amp circuits.
- 15k lumen 2' linear LED highbays, 7x5 arrangement identical to above but one fewer fixture per rafter. Would be wired similarly.
- 6-lamp T8 highbays (e.g. Lithonia IBZ), 7x6 arrangement identical to the 12k lm LED setup. These would be using linear LED bulbs.
The questions I have are:
a) Are the 12k lumen or 15k lumen fixtures better for this application with a ~14' mounting height? 14' seems to be in a gray area where there doesn't seem to be a clear recommendation as to which one is better.
b) Are the integrated LED fixtures or replaceable-bulb linear LED fixtures recommended? I am a little leery of getting an integrated LED fixture because if something fails, the entire fixture must be replaced and it would be very likely that whatever new fixture is available at the time would be dissimilar to the ones already in use. I did a bunch of reading on this topic and nobody ever seemed to answer the question.
3. I will have outdoor lights over the overhead doors. I would like to have this on a switch controlled inside of the house so I can see to go outside there in the dark but not have the place lit up every night using a dusk to dawn light/lights. Since the building will nearly certainly be supplied from the pole rather than being a subpanel from the house, would it be worthwhile to do this the conventional way of running a conduit to the house for a separate outdoor lighting circuit or would another means such as a remote-controlled switch be better, and if so, which one?
Thank you for your input.