When I wired my new shop, I located all the boxes with the little built-in "nubs" that space them out from the stud properly for 1/2" drywall.

I've since decided I'd like to install 19/32" (nearly 5/8") T1-11 for interior wall covering.

This means that all the wall plates will "stand out" from the box about an 1/8" more than intended, exposing some wood to possible arcing and sparking.

This strikes me as a possible fire hazard.

Am I over thinking this?

Are there "special" outlet and switch plates that handle this issue?

Should I bite the bullet and relocate the boxes out from the stud a little more?
 
To avoid these ads, REGISTER NOW!

ThomasP

Well-known member
Joined
Oct 16, 2014
Messages
134
If your devices are "arcing and sparking", you have a much bigger problem on your hands.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Since you are installing in a combustible material, NEC 314.20 requires that the boxes be mounted flush with the surface, so the face plates will draw down on the box and device properly. In NON-combustible materials, such as sheetrock, tile, etc, the box is allowed to be recessed as much as ¼" (which is a poor practice, and looks crappy).

Charles
 

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
It appears to me that those box extenders significantly reduce the available volume inside the box. If the box is filled to near capacity, this will become an issue. Perhaps you can trim them if you're only needing to extend a fraction of an inch or so.
 

Blk88GT

Well-known member
Joined
Mar 16, 2009
Messages
1,077
Location
Manitoba
I can't see how trimming them would still pass code, but it would certainly work in the case you're describing.
 
To avoid these ads, REGISTER NOW!

joe_padavano

Well-known member
Joined
Feb 26, 2011
Messages
1,788
Location
Northern VA
I can't see how trimming them would still pass code, but it would certainly work in the case you're describing.

The overfilled box shouldn't pass code either. In any case, If you trim them to the point that there is still the same minimum overlap to the original box that the design allows (since the extender is designed to accommodate a range of wall covering thicknesses), how does that change the functionality of the extender? The OP is only talking about 1/8" or so of required extension, and these things accommodate 1.5" of extra thickness.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,588
Location
Fullerton, CA
They're so thin that they don't have an appreciable effect on the volume of the box.


They're allowed to be trimmed and not violate the listing.
 
Last edited:

Rock knocker

Well-known member
Joined
Aug 14, 2014
Messages
704
The steel ones aren't UL listed, at least in the US
Thomas Betts and Gavin both make steel extensions available in the US. The Gavin product is stated to be UL listed on their site, while I find it hard to believe that TB would sell an item in the USA that was not listed if applicable
 