First post in forum - lift motor help.

joey1320

Well-known member
Joined
Jun 14, 2015
Messages
1,813
Location
NE Ohio
Hello everyone, lomg time lurker first time poster ;)

So I have an issue and I hope I can pick your brains while I wait for technical support to get back to me tomorrow(I hope). After much reading and researching I went ahead and ordered the Harbor Freight Mid-rise scissor lift.
http://www.harborfreight.com/6000-lb-capacity-scissor-lift-91315.html

The lift arrived on Wednesday and over the past two days my father and I ran the 240v wiring from the house to the garage. We have 117.3v at each "hot" lead on the NEMA 6-20p plug, so we know the wiring from the house is good. When we plug in the motor and try to use it, nothing happens. So the search and rescue mission begins...

The motor is a 2HP, single Phase, 3450rpm, 220v unit from SMC.
This is the USA website and my model number isn't listed YCN 5662-4k. But the Chinese one shows it, its all in Chinese though.
http://smcnorthamerica.com/stainlessmotors

The first thing we did was check the on/off switch. Continuity at the switch is correct - 0 resistance when pushed in, infinite when released.

Next we started checking the wiring. We had removed the switch panel to check the switch, and now we had access to the wires.

*Green lead is ground, which is secured to the case of the motor and has continuity to ground.

*White voltage wire splits into two other leads, which run into the motor case. These two wires are yellow.

*Black voltage wire goes to the on/off switch.

*The other side of the switch comes from inside the motor case. There are another two yellow wires, that connect into one wire, which screws to the switch.

As you can see we have four yellow wires that go into the motor case. Two of these wires go to the capacitor, the other two, we think go to the motor itself. Are we correct? (Unfortuantely we didn't remove the case of the motor, since I don't want to ruin my warranty)

So to recap -
Ground to screw in case.
Hot lead to 2 wire split - into case.
Hot lead to on/off switch.

Now here's what we were able to determine after testing.
When the plug is connected to the outlet, all of the wires besides ground, are hot. All meassure 117v, without the on/off switch being pressed.

The hot lead that goes to the on off switch meassure 117v.(obvious)

The other side of the switch, without the switch being pressed, meassures 117v.

The two yellow leads that go to the capacitor meassure 117v.

The lead that comes from the motor, which is supposed to go to the opposite side of the on/off switch has 117v.

I also disconnected one of the yellow wires that go to the capacitor, and with it disconnected I still read 117v on it.


As you can guess we're a bit confused here...
Questions:

Has anybdy had any experience with this type of electrical issue on these motors?

If anyone here has one of these lifts, would you be willing to remove the panel and take a few pictures or voltage readings?

Is there anything that sticks out that we did wrong or didn't test right?


Thank you for the time. I plan on taking pics tomorrow and posting them. I'm also waiting for the response from technical support, so we will see.
:thumbup:
 
To avoid these ads, REGISTER NOW!

MTW

Well-known member
Joined
Aug 6, 2013
Messages
294
Location
SE Michigan
The lift arrived on Wednesday and over the past two days my father and I ran the 240v wiring from the house to the garage. We have 117.3v at each "hot" lead on the NEMA 6-20p plug, so we know the wiring from the house is good. When we plug in the motor and try to use it, nothing happens. So the search and rescue mission begins...

The motor is a 2HP, single Phase, 3450rpm, 220v unit from SMC

I would assume this is where your problem lies. Lift is rated for 240V, but all you measure is 117V. The lift is looking for 240V from line to line, it doesn't care what your line to ground voltage is. Measure the line to line voltage, before you assume your wiring is correct.

MTW Ω
 
To avoid these ads, REGISTER NOW!

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,271
Location
Penngrove, California
As suggested, it sounds like you have two of the same "phase". Go back to your breaker pair feeding this circuit, (you do have a pair of tied handle breakers?), and measure from the output side of each of them, one to the other, to confirm 240VAC.
 

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
... We have 117.3v at each "hot" lead on the NEMA 6-20p plug, so we know the wiring from the house is good. ...
:thumbup:

So how many volts between the two 'hot' leads? Zero or about 235?


I would assume this is where your problem lies. Lift is rated for 240V, but all you measure is 117V. The lift is looking for 240V from line to line, it doesn't care what your line to ground voltage is. Measure the line to line voltage, before you assume your wiring is correct.

MTW Ω

MTW gets it!

Your 240 breaker that you feed this line with is wrong. Or did you just use two random breakers?
 
OP
J

joey1320

Well-known member
Joined
Jun 14, 2015
Messages
1,813
Location
NE Ohio
Thanks for the replies guys. I went out to the garage, meassured the voltage at both hot leads and got 232v combined, and yes we are using a dual pole 20a breaker ;)

Lucky me Harbor Freight got back to me rather quickly and they recommended rewiring the yellow leads going to the capacitor, apparently they were crossed. Glad nothing major happened but kind of surprised the company didn't test the motor after assembly. Oh well it is what it is...

And here it is ;) Sorry for the extra large crappy pic.
Now I need to organize the garage a bit better and start using it.