First time - shorted circuit

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,971
Location
Thousand Islands NYS
I think I've been vigilant and careful in my many years of diy electrical work. (Well, overlooking my grad school time 50 years ago when I'd tie portable dimmer boards - theatre lighting - into panels - hot.) Seems I must have put a drywall screw or nail into a piece of 14/3 NM-B. Popped a breaker first time I hooked up. Then worked fine for three days. Then dead short.

Is it possible the 2-screw clamp caused the problem?

About to try to diagnose and replace wire before cellulose is blown in attic tomorrow.
 
To avoid these ads, REGISTER NOW!

Copymutt

Well-known member
Joined
Sep 3, 2016
Messages
3,403
Location
Colorado
Not likely, box entry clamps are designed to do their job. Most likely your first guess. New work? Disconnect from breaker box & begin the search. If multiple devices break those connection at their junction boxes & meter each till its narrowed down.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,849
Location
Richmond, VA
I had a clamp short out a wire on a wafer led a few years ago. 100% my fault in installation, but it did cause a problem.

Good luck with finding it
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,996
Location
Central Iowa
If the clamp is too tight, yes it will cause a short. Is this your addition? If it's an arc fault, it might be something else. The very first time I turned on an arc fault breaker it tripped. Upon opening every single box on the circuit, I discovered a ground wire had folded back wrong and was touching the neutral on a receptacle. It could be something as simple as that. If it is an arc fault breaker, take it out and try using a regular breaker just for diagnostics. If it still trips, you have a real short. If it doesn't, it's the arc fault seeing something it doesn't like.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,849
Location
Richmond, VA
If the clamp is too tight, yes it will cause a short. Is this your addition? If it's an arc fault, it might be something else. The very first time I turned on an arc fault breaker it tripped. Upon opening every single box on the circuit, I discovered a ground wire had folded back wrong and was touching the neutral on a receptacle. It could be something as simple as that. If it is an arc fault breaker, take it out and try using a regular breaker just for diagnostics. If it still trips, you have a real short. If it doesn't, it's the arc fault seeing something it doesn't like.
You feeling OK?

First time I've seen you type out arc fault without a suggestion to throw it away
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,291
Location
Illinois near St. Louis, Missouri
Narrow it down to which run of wire by disconnecting the joints - guessing you may have already done that. Check the end points. If nothing obvious there then does it go through holes where it might be caught by a nail/screw. Pull the wire back and forth a bit to check if it is free to move at each member - if it is free there isn't a nail puncture there. Or are there portions of the runs already behind drywall and other things? If it's a hard short then I would break out the TDR to find distance to the short but that's not something most people have...
 
To avoid these ads, REGISTER NOW!
OP
B

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,971
Location
Thousand Islands NYS
Well, found it. New wiring in previously unfinished garage. Is not now but will be arc fault - actually combo arc fault GFCI breaker not installed yet.

Potentially 5 segments and the short - using a vom meter - did not seem to be constant, but always between hot and ground. I *think* it was one strand of a stranded 16 in a fixture was not fully in the wire nut. Retesting and wiggling and jiggling every wire at 4 boxes, and of course looking for continuity between every combination of conductors, working again.

Makes a case for taping all wire nut connections, or at least those with stranded wire. I have generally not, disliking the leftover goo when I have to change it. Makes me fond of the wago like connectors included with some fixtures. Stranded 16 wire nutted to solid 14 or 12 is not my favorite.

Discouraging because I don't ever recall making this mistake before. Work done outside on a ladder in 40 degrees so numb fingers along with age contributed.

Thank you all for your thoughts.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,291
Location
Illinois near St. Louis, Missouri
A meter may give inconsistent results if it is not a "hard" short, meaning the conductors are in good contact. If they aren't in good contact, even a microscopic distance between, the low voltage of the meter will not jump the gap but with line voltage it will jump the gap. I hate the goo from tape when you have to go back later.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,032
Location
Coronado, CA
One house I bought had a problem, it turned out to be the Lag Bolt for the seismic restraint ******** a water heater had penetrated the NM Cable feeding a receptacle.

Backed out the Lag and reinstalled it 2" higher, put some liquid electrical tape on the cable, then patched the drywall.
 
OP
B

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,971
Location
Thousand Islands NYS
One house I bought had a problem, it turned out to be the Lag Bolt for the seismic restraint ******** a water heater had penetrated the NM Cable feeding a receptacle.

Backed out the Lag and reinstalled it 2" higher, put some liquid electrical tape on the cable, then patched the drywall.
oh no, don't admit to that in writing!
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
One house I bought had a problem, it turned out to be the Lag Bolt for the seismic restraint ******** a water heater had penetrated the NM Cable feeding a receptacle.

Backed out the Lag and reinstalled it 2" higher, put some liquid electrical tape on the cable, then patched the drywall.
That wasnt a good idea. You cant tell if the conductors were damaged which they most likely were
 