Flat roof penetration for multiple linesets?

bzinsky

Well-known member
Joined
Oct 27, 2014
Messages
5,565
So I'm looking for something that I run 3-6 sets of AC linesets and corresponding electric through a torch down flat roof. Not sure how to go about that. They will immediately spread out once the are on the roof, so running a length of flexible conduit to house all of the lines isn't really what I'm looking for. I want to keep lineset lengths to a minimum since I'm close to the limit.

That being said, what's the best type of penetration I can use?

I was looking at gooseneck vents, something like this
ar130609134921194.jpg


I have never seen AC linesets and electrical just being ran out of them though, not sure if it's a good idea.

Most of the vents that are commonly used seem to be too small for what I need. Not looking to have a ton of penetrations for obvious reasons.

Any ideas?

Also, it's the Philadelphia region, the most snow I've ever seen on the ground is about 36" if that's relevant.
 
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
Look up best materials .com, I'd link if i knew how, lots of roofing materials and tons of options.
 

BlackTalon

Well-known member
Joined
Aug 22, 2014
Messages
183
Location
Alexandria, VA
A gooseneck like that is pretty close to what SMACNA and NRCA recommend. It's best to put in a real curb (treated wood is fine) and flash that with mod bit base flashing. then you fabricate/ install essentailly a sheet metal gooseneck that you route the service lines through. While I have seen a regular gooseneck like the one you show be used, it is better to fab it with a one-way-sloped top instead of an arched top, as you can loose-lock the sloped top all around so it is easily removable if/ when lines need to be changed down the road. Might want to contact a local commercial roofer that has a competant sheet metal shop; they should have some idea of how to fabricate such an enclosure.

Alternately, if you have sheet metal braking/ bending capabilities yourself shoot me a PM with your email address and I can scan/ email you the SMACNA/ NRCA detail so you can see how the pieces need to be formed and assembled.
 

RivennHewn

Well-known member
Joined
Jun 4, 2011
Messages
10,372
Location
PNW
I just did couple for condensate units for some walk-in coolers.

I just built up a curb out of PT 2x12s. I made sure that they were high enough above the roof for snow/ice load.

The roofing goes up and over the edge, then the sheet metal cover will be built to hang down about 5". Can post pics next week.
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,609
Location
Long Island
I've only seen it done one way. You put in a curb, extend your roofing up the sides (being careful to not cut square corners that will start a tear), flash up the sides and over the top, pass the lines through the open middle and fill around the lines with a pourable sealant. Look up a "pitch pocket".
 

sickjuice

Well-known member
Joined
Jun 12, 2012
Messages
143
Location
welfare provence
Pitch box. Build a box, extend the roof membrane up, run lines, stuff with insulation, and cap with metal (preferred) or more roof membrane

Never seen witch hats used on linesets. IMO I think the insulation would wick water
 

Attachments

  • photo-2.jpg
    photo-2.jpg
    158.3 KB · Views: 24
  • td.jpg
    td.jpg
    37.2 KB · Views: 27
Last edited: