Flex conduit for "long" 120 runs?

jragain

Member
Joined
Feb 5, 2011
Messages
14
I have two 120V circuits in my garage that are currently surface mounted in EMT. I want to change their routes. Each new run would be about 40-50 feet long. I have access to a couple hundred feet of free flex conduit, but I want to keep things safe and legal. Am I OK to use flex for the entire run(s), or do I need to buy the EMT and get out the bender? Thanks.
 
To avoid these ads, REGISTER NOW!

Delta74

Well-known member
Joined
May 6, 2011
Messages
320
Location
Peachland B.C. Canada
If this is the Flex i am thinking about, better check your codes, usually you are restricted to no more then 6 feet, if its BX ( ac-90 ) has the wires in it, you could run thousands of feet no problem, just use the anti-shorts, and proper connectors, and no problems.
 

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
there is no NEC requirement that i can remember on length of FMC.


i will say this though, if you plan to install the FMC then pull wire, it will be a major PITA.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
If flex/greenfield is used, plan on running a grounding conductor too....
 
To avoid these ads, REGISTER NOW!

wanna_be

Member
Joined
Sep 1, 2005
Messages
7
Location
Alabama
I believe the 6' is only when it is unsecured. Like a drop going to light fixture or something like that.
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
I bet you could sell the flex and make enough money to buy the EMT and some of the wire.....

Someone did a bunch of wiring in my in-laws garage using flex....looks like **** and is hanging down.....something else to fix for them when I get time.
 

Adrien

Well-known member
Joined
Mar 17, 2011
Messages
317
Location
Taft, CA
If this is the Flex i am thinking about, better check your codes, usually you are restricted to no more then 6 feet, if its BX ( ac-90 ) has the wires in it, you could run thousands of feet no problem, just use the anti-shorts, and proper connectors, and no problems.

Incorrect. There's no limit on the length of Flexible Metal Conduit.

there is no NEC requirement that i can remember on length of FMC.

i will say this though, if you plan to install the FMC then pull wire, it will be a major PITA.

Correct.

If flex/greenfield is used, plan on running a grounding conductor too....

An Equipment Grounding Conductor is only required if it's to remain flexible and not securely fastened. If it's not to remain flexible the FMC can be used as the Equipment Grounding Conductor.

I believe the 6' is only when it is unsecured. Like a drop going to light fixture or something like that.

Correct.

I bet you could sell the flex and make enough money to buy the EMT and some of the wire.....

Someone did a bunch of wiring in my in-laws garage using flex....looks like **** and is hanging down.....something else to fix for them when I get time.

Also correct. :D

Also, if you do decide to run the FMC it needs to be secured 12" from each termination and also every 4.5'.

Adrien
 

dwilliams35

Well-known member
Joined
Sep 27, 2008
Messages
271
Location
Pattison, TX
My code book's at work, but as I remember the main thing about the 6' is the grounding: if you've got a separate grounding conductor in the conduit, all you have to worry about is securing it. I'd go back with EMT myself. Just looks better, and EMT is pretty cheap.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Incorrect. There's no limit on the length of Flexible Metal Conduit.



Correct.



An Equipment Grounding Conductor is only required if it's to remain flexible and not securely fastened. If it's not to remain flexible the FMC can be used as the Equipment Grounding Conductor.



Correct.



Also correct. :D

Also, if you do decide to run the FMC it needs to be secured 12" from each termination and also every 4.5'.

Adrien

If in excess of 6 feet a ECG must be used the greenfield is no longer suitable for a grounding path.
 

klhitman

Well-known member
Joined
Sep 17, 2010
Messages
1,016
Location
pewee valley
we were running some through some hvac units at work and some engineers came in and said the the runs could only be 4ft long by code. me and the guy i work with tried to argue that we never seen that in the code book. but we had to fix it or they wouldn't buy the unit. so to this day we run everything in EMT unless its 4ft or less.
 