I need to run some 6/3 wire from my switch to my compressor. Because of vibration I don't want conduit. I looked at some armored cable but the smallest I could find was 25'. I only need a few feet. Ideas? thanks
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,022
Location
Modesto, CA
I need to run some 6/3 wire from my switch to my compressor. Because of vibration I don't want conduit. I looked at some armored cable but the smallest I could find was 25'. I only need a few feet. Ideas? thanks
need to back up here

#6 is very large for a compressor motor... 10HP only needs #8...

what is the HP rating of the motor?

what kind of switch are we talking about? the pressure switch? disconnect switch?
 
Last edited:

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
Plenty of flexible metallic or non products readily available for this type of installation at even the crappiest hardware store in the middle of nowhere, if it is some kind of mystery, should you really be trying this yourself?
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,005
Location
VT
Ignoring the wire size issue, premade AC sealtite whips are like $25 at the box store.

You can also get just the sealtite, fittings and buy wire by the foot at box stores.
 

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
You can buy SO cable by the foot at Home Depot.... At least at my local store, anyway.

There is no minimum. You can buy as little as one foot if you would like.
 
To avoid these ads, REGISTER NOW!

pancho400cid

Well-known member
Joined
Sep 26, 2014
Messages
4,516
Location
Austin, TX
I don't know the code legalities of exposed SO cable. Is the wire in conduit up to the compressor? If so, mount a box on the wall near the compressor. Run rigid/EMT conduit to the box, and seal-tite flex conduit from the box to the pressure switch or motor lead box on the compressor.

...
 

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,221
Location
Denver, CO
I don't know the code legalities of exposed SO cable. Is the wire in conduit up to the compressor? If so, mount a box on the wall near the compressor. Run rigid/EMT conduit to the box, and seal-tite flex conduit from the box to the pressure switch or motor lead box on the compressor.

...
SO cable is flexible power cord. Designed to be exposed... People are suggesting this from the box to compressor.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,952
Location
NJ
If this is a single-motor-only branch circuit, then motor over-current protection rules apply. The conductor sizing will be based on the motor hp and not the CB size.

You may even be able to use 10-3 SO cord. Need the pic of the motor nameplate to be certain.
 